15 to 22mm ?

by jazzy220 » Wed Oct 27, 2010 4:47 pm

Hi I have a 15mm mains cold water supply going directly to a hot water heater in the kitchen, electric shower, and of course toilet and 2 sinks in total. I am re routing the pipework (new kitchen) so would there be any reason at all for stepping up to 22mm along the run and if so why.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Thu Oct 28, 2010 12:01 pm

No need at all - as you say the feed to the heater is 15mm - so you can't get more water out than what you put in .


htg