my 9.5kw shower is protected by a 50amp mcb on a rcd shower unit, is this correct or should it have a 45amp instead, will this have to be changed or is it o.k the way it is.

Grateful for any reply.
Rank: Labourer
Progress to next rank:
Posts: 1
Joined: Tue May 22, 2007 1:34 pm


Simply Build It

Postby sparx » Tue May 22, 2007 11:39 pm

hi, your shower will draw 41.3A at 230V so 45 A mcb will give closer protection in case of fault, depends on cable size & method of instalation whether 50A mcb ok, EG 10mm2 cable enclosed in wall only rated 43A, but if in surface trunking is rated 52A or 'clipped direct' on surface good for 63A, not allowing for volt drop due to length of run!
Easy being sparky eh!
regards SPARX
Rank: Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

Display posts from previous
Sort by
Order by

  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!