Add Radiator in attic room


Postby smevers » Wed Aug 13, 2008 8:15 am

I plan to add a radiator into my attic room and run it off the 1st floor central heating loop. It will be a smallish rad. Is there any reason I cannot just add it onto the end of the existing loop - My main concern is whther the addition height will cause problems.

Thanks
smevers
Rank: Labourer
Progress to next rank:
50%
Posts: 3
Joined: Wed Aug 13, 2008 8:05 am

Sponsor

Simply Build It

Postby AdamsHeating » Wed Aug 13, 2008 12:41 pm

Hiya,

I can't see there being a problem, if you have enough water pressure to fill your system already and your boiler output is sufficient to take another radiator (total output of rads must be less than or equal to total output of boiler) then adding an extra rad should be fine, just T in. You may need to throttle the lock shields a little to get the balance right to force the hot water up there.
AdamsHeating
Rank: Ganger
Progress to next rank:
47.3%
Posts: 121
Joined: Fri Aug 08, 2008 10:49 am

Postby htg engineer » Wed Aug 13, 2008 7:12 pm

It depends on the type of system you have..........



htg
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Postby smevers » Thu Aug 14, 2008 7:28 am

The system is conventional boiler with hot water cylinder.

Thanks
smevers
Rank: Labourer
Progress to next rank:
50%
Posts: 3
Joined: Wed Aug 13, 2008 8:05 am

Postby htg engineer » Thu Aug 14, 2008 2:23 pm

The F&E tank will have to be sited above the radiator you add to the attic.

Then the vent pipe should be 18" above the tank - is there room ?

Also it may be possible you will have to update the pump, and possible get a 6m head pump rather than 5m, best way to find out is to try it with the existing pump first.


Htg
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Postby Dave From Leeds » Fri Aug 22, 2008 12:38 am

Htg engineer, just out of interest why does the vent pipe need to go 18" above the F&E tank? Presumably it's to allow for expansion when the water gets hot. However, water will equalise level between the tank and the vent pipe. I would have thought the critical issue here would be to allow sufficient space in the F&E tank between the water level when cold and the overflow outlet from the tank and that, provided that the vent pipe goes over the top of the tank and it's open end is higher than the overflow, it would be OK.
Dave From Leeds
Rank: Ganger
Progress to next rank:
86%
Posts: 179
Joined: Mon Nov 19, 2007 9:02 pm

Postby htg engineer » Sun Aug 24, 2008 9:55 am

The minimum recommended height is 450mm.

Recommended calculation to determine the open vent height :

150mm (vent height required above tank water line) + 40mm per metre of system height.

450mm = 17.7" (18"ish)

It allows for expansion, but also the extra height will prevent pumping over and air being drawn into the system via the vent pipe, as does the position of the pump and the cold feed.

htg
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Postby Dave From Leeds » Tue Aug 26, 2008 11:43 pm

Thank you for the information Htg Engineer.
Dave From Leeds
Rank: Ganger
Progress to next rank:
86%
Posts: 179
Joined: Mon Nov 19, 2007 9:02 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 