Another Ceiling light problem..me again!

by emtthegreatone » Tue Dec 18, 2007 12:33 pm

OMG! have got my 3 reds in seperate block....earth to earth...have tried the 3 blacks in all permutations (no red sleeve!) and still no lights! any advice would be very helpful..all other downstairs light still work but nothing in lounge.........thanks in advance for any help. STOP PRESS! now have 1 light working (the one with millions of wires!) but the other as dead as a dead thing any advice on this PLEASE :-)

BLAKEY1963
Site Agent
Site Agent
Posts: 684
Joined: Wed Jun 13, 2007 11:57 pm

Re: Another Ceiling light problem..me again!

by BLAKEY1963 » Wed Dec 26, 2007 10:38 pm

[quote="emtthegreatone"]OMG! have got my 3 reds in seperate block....earth to earth...have tried the 3 blacks in all permutations (no red sleeve!) and still no lights! any advice would be very helpful..all other downstairs light still work but nothing in lounge.........thanks in advance for any help. STOP PRESS! now have 1 light working (the one with millions of wires!) but the other as dead as a dead thing any advice on this PLEASE :-)[/quote]

emtthegreatone
get in an electrcian to check things over 4 u

BLAKEY1963

ericmark

by ericmark » Wed Jan 02, 2008 10:18 am

One I did earlier in Blue Peter style. Regular question:- How does one wire a ceiling rose? The switch wires should be both red or at least have a red sleeve but in practice this is rarely the case. This is how to work out which black/Blue wire is which when all three cables are the same colours. These are:- The feed, The Switch, The next Lamp. Easy way is meter or buzzer across the cables with power all off and flick light switch until switch wire is found but often the DIY man has no meter or buzzer so next method.
Do not use energy saving bulbs as we need to be able to see bulbs working on half power use normal bulbs only. Do not use this method if you have dimmers or discharge lamps in any of the house lights.
1. With power off connect all cables except for neutrals and switch cable i.e. the black or blue are left disconnected. Put one into spare block connecter and other two in the two outer connectors of the ceiling rose i.e. one to each wire feeding lamp. Now turn on power and try if it works jump to 4. If not turn off power.
2. Swap either of two blacks (or blues) connected with one in spare block connecter and then turn on power again. If it works then jump to 4. If not turn off power.
3. Swap the wire in spare block connector with other black (or blue) in ceiling rose. It should now work one switched on again. If not there is another fault not at rose and it is beyond this simple check.
4. Turn off power again and mark cable in spare block connector with black or blue type or some other way to find it again. Then put it in spare hole with other Black (or blue) then turn on power.
5. Test all lights if all work OK then all is done on the other hand you may find odd things happening like with light you have been working on being switched on other lights don’t work and with it off the other lights work as glow only and light you were working on will also start to glow. If this is the case switch off power and swap the two unmarked black (or blue) wires. Now all should work.
So what are we doing? Well we can’t connect any of the three blacks (or blue) together as one is live when switched on so to start with we find out which wire connects to the next rose in circuit by time 1, 2, and 3 have been completed we know this is wire is spare block connector. At this point, we don’t know which of the other two blacks (or blue) is neutral and which is the switch wire. But if we connect the next lamp in series to switch instead of neutral it will do no harm but the next lamp can only get a return through the lamp in the light we have been working on so either the one we were working on will come on dim or the next in line will come on dim which is all to do with what size bulbs are fitted. But we now know exactly which two wires are the wrong way around. So finally we have in the eight holes in rose (earths normally under clamp screw) Feed to lamp, Feed from switch, break, Three live wires at all times all red or brown (one feed, one out to switch and one to next lamp), break, Neutral (in or out), Neutral (out or in), Neutral to lamp.

Look at projects one picture can be worth a thousand words. If your not sure better to get an electrician. Remember ceiling roses have live wires even when lights are switched off so always isolate at the consumer unit.