ariston leak
i have an ariston system boiler with a small leak from the pressure relief valve, which over a few days allows the pressure to drop and thus the boiler locks out, then i have to top it back up has anyone got any ideas?
If pressure is not too high, then the pressure relief valve is passing.
Try opening pressure relief valve a few times, this can sometimes re-seat them. If not, replace pressure relief valve - normally straight forward.
ariston leak
pressure increases to above 3 bar then the pressure valve opens even more
Possibly a problem with the expansion vessel.
Look in this forum at posts by andy2010
Can sometimes be re-pressurised to 1.0bar using a foot pump or similar.
Drain boiler so there's no pressure - lock open the pressure relief valve, Then pump to 1.0bar and refill system. See if there's air at the valve on the expansion vessel. The valve looks like a one off a car or bike, If there's air then re-pressurising may work, if there's water then a new expansion vessel is required.