Balancing Radiators


Postby gotabelt » Sun Dec 04, 2011 2:20 pm

Can anyone give me any advise on how to balance radiators? Being an engineer I would assume that those nearest the boiler would not have the lockshield valves open as much as those furthest away. Am I on the right track?

Peter
gotabelt
Posts: 31
Joined: Sun Dec 16, 2007 5:50 pm

Sponsor

Simply Build It

Postby plumbbob » Sun Dec 04, 2011 3:21 pm

gotabelt wrote: I would assume that those nearest the boiler would not have the lockshield valves open as much as those furthest away. Am I on the right track?

Peter


That is one of the considerations. Generally, you crack open half to a full turn the lockshield valve on the hottest radiators leaving the cold rads fully open.

More help here.

http://www.diydoctor.org.uk/projects/balancingcentralheatingsystems.htm
plumbbob
Posts: 1833
Joined: Wed May 07, 2008 9:59 pm