Bathroom fan duct outlet inside roofspace - your views?


Postby midknight » Fri Mar 20, 2009 5:00 pm

On several new terraced houses the extractor fan pvc flexible ducting is terminating in the space above the soffit and under the tiles. There are no roof vent tiles or external grilles fitted on the soffit itself.

This is for the bathroom and en-suite shower room.

There is the soffit trickle ventilation slots all the way along the soffit.

Do you think this is good enough?
midknight
Posts: 17
Joined: Wed Sep 10, 2008 8:28 am

Sponsor

Simply Build It

Postby rosebery » Fri Mar 20, 2009 9:35 pm

"On several new terraced houses"

Personally I'd suggest no on a practical level but the Building Inspector must have seen it and passed it as complying with regs.

Cheers
rosebery
Posts: 2022
Joined: Wed Sep 26, 2007 8:55 pm


Postby eljaybee » Sun Mar 22, 2009 5:23 pm

It is incorrect - the extractor should terminate to the external air not within the roof space.

I wouldn't rely upon the fact the Building Control have seen it, as it may be that the house has never had a completion or that it got missed if looked like went to an eaves vent.
eljaybee
Posts: 78
Joined: Sun Jun 22, 2008 11:53 am


Postby rosebery » Sun Mar 22, 2009 8:48 pm

"I wouldn't rely upon the fact the Building Control have seen it, as it may be that the house has never had a completion or that it got missed if looked like went to an eaves vent."

Lest my somewhat tongue in cheek comment be taken as saying its OK I did actually say No it isn't good enough.

Cheers
rosebery
Posts: 2022
Joined: Wed Sep 26, 2007 8:55 pm