boiler ideal mexico 2 honeywell


Postby kevcrabtree » Tue May 08, 2007 8:05 pm

wont ignite had problem before need to know start up sequence please
kevcrabtree
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Tue May 08, 2007 7:58 pm

Sponsor

Simply Build It

Postby Paul Pepper » Sun May 13, 2007 4:42 pm

Which model - there's a lot of different types - GC no off data badge would help!
Paul Pepper
Rank: Tradesman
Progress to next rank:
53.8%
Posts: 38
Joined: Fri May 11, 2007 6:02 pm

Postby kevcrabtree » Sun May 13, 2007 5:42 pm

thanks paul the the number is 41-429-49. any help appreciated
kevcrabtree
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Tue May 08, 2007 7:58 pm

Postby Paul Pepper » Tue May 15, 2007 6:06 pm

Sorry to be so long replying1

Assuming pilot is lit and there is 240v live into the boiler from system controls, check for 240v live on gas valve terminals. If no power present - boiler thermostat is prob at fault. If live present, gas valve prob duff.

Hope this helps!

Paul
Paul Pepper
Rank: Tradesman
Progress to next rank:
53.8%
Posts: 38
Joined: Fri May 11, 2007 6:02 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 