Bosch 24i boiler


Postby vince cahill » Mon Dec 08, 2008 11:38 am

:? pressure indicator drops over a period of 2 days. Noticed water comes from somewhere inside boiler. Placed bucket underneath to prove. Water not coming from water top valves. Heating and hot water ok. Can anyone point me in the right direction? Thanks
vince cahill
Posts: 3
Joined: Mon Dec 08, 2008 11:22 am

Sponsor

Simply Build It

Postby Steve the gas » Tue Dec 09, 2008 6:20 am

Hi Vince,

Could be the PRV blowing excess pressure off, if not connected to outside it will come from your boiler. As an aside is your filling loop def. shut?
Steve
Steve the gas
Posts: 780
Joined: Sun May 04, 2008 7:07 am


Postby vince cahill » Tue Dec 09, 2008 11:58 am

[quote="Steve the gas"]Hi Vince,

Could be the PRV blowing excess pressure off, if not connected to outside it will come from your boiler. As an aside is your filling loop def. shut?
Steve[/quote]
Thanks for your response Steve much appreciated. The loop is switched off and I removed flexi pipe to ensure both valves were shut.
As for as I am aware all is connected to boiler, will this problem cause me any severe problems. Once again thanks. Vince
vince cahill
Posts: 3
Joined: Mon Dec 08, 2008 11:22 am


Postby Steve the gas » Wed Dec 10, 2008 5:21 am

Well,

You need to locate the leak - it cannot be good in the long run.

It could be a fitting coming loose or a fitting/washer beginning to fail etc.
Steve the gas
Posts: 780
Joined: Sun May 04, 2008 7:07 am


Postby vince cahill » Thu Dec 11, 2008 12:26 pm

[quote="Steve the gas"]Well,

You need to locate the leak - it cannot be good in the long run.

It could be a fitting coming loose or a fitting/washer beginning to fail etc.[/quote]
Thanks again i will have a look around. Maybe time to get a fitter out
vince cahill
Posts: 3
Joined: Mon Dec 08, 2008 11:22 am