Price Doctor - Extension quote and price checking software

The Southern Homebuilding and Renovating Show 2013, Sandown Park, Surrey


DIYDoctor
DIYDoctor
Home   Contact   DIY How-to Projects
  • Forum Index
  • FAQ
  • Search
  • Login
  • Register
  • Board index ‹ DIY and Home Improvement Forums ‹ Central Heating & Air conditioning & Ventilation
  • FOLLOW US
    Twitter Logo Facebook Logo YouTube Logo
    • HOME
    • DIY PROJECTS
    • DIY TIPS AND TRICKS
    • REVIEWS
    • GARDENING
    • DIY VIDEOS
    • GREEN LIVING
    • HIPS
    • FIND TRADESMEN
    • PRICE DOCTOR
    • FORUM
    • BLOG
    • NEWS LETTER SIGNUP
    • SHOP
    • SUPPLIERS
    • ADVERTISE HERE
    • PRESS



     
    Recommend This Page
    Tweet



    #
    Trustmark and the NHIC
    DIY Doctor are
    members of:

    National Home Improvement Council
    Trustmark - Government Endorsed Standards
    #



    Can someone help me solve a problem








    Post a reply




    12 posts • Page 1 of 1

    Can someone help me solve a problem

    Postby dbwoody » Tue Mar 06, 2012 1:24 pm

    My central heating system is Pumped Open Vented with 3 way diverter valve for heating water tank. I was working in the boiler area and could hear what sounded like boiling water coming from the boiler, wooshing and gushing, when I checked I found that hot water was being pushed up the vent to the header tank with a slight amount coming from the overflow pipe, the pump appeard to be running and both heating and hotwater stats were calling.

    Anyone got any ideas???
    dbwoody
     
    Posts: 8
    Joined: Tue Mar 06, 2012 12:45 pm
    Top

    Re: Can someone help me solve a problem

    Postby plumbbob » Tue Mar 06, 2012 11:02 pm

    Water should never be coming out of the expansion vent pipe if the heating is working correctly. The question is though; was the water boiling or not?

    How hot is the header tank?

    Normally boiling water would be associated with loud knocking and banging noises.
    plumbbob
     
    Posts: 1806
    Joined: Wed May 07, 2008 9:59 pm
    Top

    Re: Can someone help me solve a problem

    Postby dbwoody » Wed Mar 07, 2012 9:20 am

    No I don't believe water was boiling it was too hot to touch the vent pipe though, it was as if the pump had stopped for some reason, it was set on speed 11 where it has been for long time, so I moved it to speed 111 and although it is a bit more noisy, especially when heating is off and only hot water is calling, it has settled down.
    dbwoody
     
    Posts: 8
    Joined: Tue Mar 06, 2012 12:45 pm
    Top

    Re: Can someone help me solve a problem

    Postby plumbbob » Wed Mar 07, 2012 4:41 pm

    Pumps generally only have three speed settings 1,2 and 3. Marked I, II, and III respectively. So by altering it from II to III, you have increased the speed to max. Now this is not an issue as nearly all systems use speed three anyway - apart from the water circulating faster, it just means the pump is noisier.

    Check the water in the header tank is not hot and the vent is not over-pumping water.

    Quite why the noise occurred originally is a little unclear.
    plumbbob
     
    Posts: 1806
    Joined: Wed May 07, 2008 9:59 pm
    Top

    Re: Can someone help me solve a problem

    Postby dbwoody » Thu Mar 08, 2012 9:05 am

    Thanks "plumbbob" for your replies, as an engineer myself I find them a bit academic, my hope was that an heating engineer who had experienced a simular problem and could offer advise.

    Thanks for tying to help.
    dbwoody
     
    Posts: 8
    Joined: Tue Mar 06, 2012 12:45 pm
    Top

    Re: Can someone help me solve a problem

    Postby plumbbob » Thu Mar 08, 2012 2:52 pm

    Finding an engineer with experience won't be a problem, but what will is trying to narrow down the possibilities of what could be happening.

    If I wrote every possibility of what might be wrong it would end up being a tome. What we need to do is try and identify more symptoms so the search can be narrowed down.
    plumbbob
     
    Posts: 1806
    Joined: Wed May 07, 2008 9:59 pm
    Top

    Re: Can someone help me solve a problem

    Postby dbwoody » Thu Mar 08, 2012 3:57 pm

    ok "plumbbob" I understand but I really suspect the Grundfos Pump, I have talked to Grundfos tech guys and they tell me that a pump performance can deteriorate over time, this pump is 11 years old and always been on speed 11 until now and was in need of a boost but speed 111 is too high so it falls between setting and Grundfos have said that it could need replacing, so I have got a new pump and will fit it this week-end and I will let you know the result.

    Thanks for your help.
    dbwoody
     
    Posts: 8
    Joined: Tue Mar 06, 2012 12:45 pm
    Top

    Re: Can someone help me solve a problem

    Postby plumbbob » Thu Mar 08, 2012 5:20 pm

    dbwoody wrote:Grundfos have said that it could need replacing, so I have got a new pump and will fit it this week.


    True,if the pump is momentarily seizing or slowing then the water trapped in the boiler will begin to boil and might make the noises you describe.

    Grunfos are also right in saying pumps can deteriorate over time, but then, many are working fine after 30 years service.

    When you drain down, use a strainer on the hose end to collect, for inspection, any large particles that might be responsible for jamming the pump.
    plumbbob
     
    Posts: 1806
    Joined: Wed May 07, 2008 9:59 pm
    Top

    Re: Can someone help me solve a problem

    Postby dbwoody » Fri Mar 09, 2012 11:41 am

    I used a strainer last week when I flushed the system and found some small debris but nothing significant but I have now installed a SPIROTRAP filter.
    dbwoody
     
    Posts: 8
    Joined: Tue Mar 06, 2012 12:45 pm
    Top

    Re: Can someone help me solve a problem

    Postby PowerFlushAssoc » Sat Mar 10, 2012 2:28 am

    This is a common problem on open vented systems. You have a hardened sludge build-up in the return pipe to the pump, because this build-up does not move around the magnetic filter you installed will not solve any problems as the sludge / problem is not mobile. The build-up is where the downfeed and vent pipe meets the return pipe. The system water is over-pumping because there is less resistance in going up the vent pipe rather than having to go through the narrowing in the return pipe, just after the vent pipe. You will have to cut out and clean this section or re-pipe that bit.
    PowerFlushAssoc
     
    Posts: 10
    Joined: Fri Nov 18, 2011 11:40 pm
    Top

    Re: Can someone help me solve a problem

    Postby dbwoody » Sat Mar 10, 2012 1:01 pm

    Thank you for your comments, I will certainly investigate, I have no problem with this area when I refilled the system after flushing though, but as I say I will cut out the pipe and have a look.
    dbwoody
     
    Posts: 8
    Joined: Tue Mar 06, 2012 12:45 pm
    Top

    Re: Can someone help me solve a problem

    Postby dbwoody » Mon Mar 12, 2012 4:40 pm

    Thanks "power flush man" you are absolutely right, I have cut out the area in question and it sure was blocked, it had been totally blocked but I managed to cut a 5mm hole through yesterday so I cut get top-up water in the system.

    When I cut out the TOWER air separator and all the pipe around it, could not believe the build-up in the air separator and pipework, the tee at the point where cold feed meets flow pipe from boiler had been totally blocked but now I have replaced all pipework.

    System is now working good without any noise and over flow problems.

    Thanks once again.
    dbwoody
     
    Posts: 8
    Joined: Tue Mar 06, 2012 12:45 pm
    Top


    Post a reply

    12 posts • Page 1 of 1

    Return to Central Heating & Air conditioning & Ventilation





     


    • { RELATED_TOPICS }
      Replies
      Views
      Last post
    • Radiator problem - unable to solve with bleeding - stuck!
      by Mikeyg » Mon Nov 26, 2007 7:29 pm
      2 Replies
      1462 Views
      Last post by paul31 View the latest post
      Tue Nov 27, 2007 1:08 pm
    • Can anyone solve this? 4 British Gas Homecare Visits Havent
      by nickgrc » Fri Dec 14, 2007 11:41 pm
      6 Replies
      2811 Views
      Last post by roger196 View the latest post
      Sun Dec 16, 2007 8:00 pm
    • CH problem - help please
      by oldbaldman » Tue Mar 10, 2009 8:50 am
      3 Replies
      1163 Views
      Last post by oldbaldman View the latest post
      Mon Mar 16, 2009 9:34 pm
    • HW and CH problem
      by ben.gale » Sun Nov 22, 2009 6:05 pm
      6 Replies
      1463 Views
      Last post by Roundstone View the latest post
      Sat Feb 13, 2010 4:06 pm
    • heating problem
      by bello » Thu May 03, 2007 11:34 am
      1 Replies
      1587 Views
      Last post by Reynoldspc View the latest post
      Sat May 05, 2007 11:14 pm

    • Board index
    • The team • Delete all board cookies • All times are UTC
    • SitemapIndex SitemapIndex
    • RSS Feed RSS Feed
    • Channel list Channel list
    Powered by phpBB® Forum Software © phpBB Group





    Diy Doctor Ltd  (Company No. 5863375)

    DIY  |  DIY How To  |  DIY Forum  |  Terms & Conditions  |  Privacy Policy  |  Cookie Info  

    © Copyright DIY Doctor Ltd 2011  Developed by Boson Media  Hosted by Rackspace