central heating combi boiler problem

by carter barter » Fri Dec 12, 2008 10:02 am

I have a Ideal C80FF combi boiler that is playing up. The problem is the presure keeps droping down to zero but when I presurise back up to 1Bar it runs ok but the preasure soon rises up to 3bar I then turn the heating off and it soon drops back down to 1Bar and below. Any Ideas?[/b]

Steve the gas
Site Agent
Site Agent
Posts: 780
Joined: Sun May 04, 2008 8:07 am

by Steve the gas » Fri Dec 12, 2008 3:34 pm

Hi,

Check the expansion vessel, it has a schrader valve,check pressure in it.
It should be 0.8 - 1 bar, diaphragm could have failed.
Don't be too worried about the 3 bar pressure the PRV will dump the water outside.

If this is worrying you - get an RGI in.

Hth

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Sat Dec 13, 2008 10:08 am

As stg says - it'll be the expansion vessel at fault. Press the valve on the expansion vessel.

Air ? re-pressurise
Water ? the diaphragm is shot and you need a new vessel.


htg