Central Heating Problems: Issues after Fitting Boiler Filters


Postby Ian Thompson » Fri Jan 11, 2013 4:58 pm

Hi
I recently had by boiler serviced and a filter fitted to the feed to collect the gunge that can build up in the pipework. Since this was done I cannot get two of the downstairs radiators( kitchen and dowstairs toilet) to work without switching off one of the upstairs ones! Ive tried bleeding the rads and increasing the water pressure intake to the boiler from 1.5 to 2 bar, but nothing has worked.
Any ideas gratefully accepted!!
Ian Thompson
Posts: 13
Joined: Thu Nov 15, 2012 2:01 pm

Sponsor

Simply Build It

Postby htg engineer » Fri Jan 11, 2013 7:51 pm

There's normally a filter in the flow pipe from the boiler. Check this is clear, as another filter has been fitted this is another restriction in the system. Clean the boiler filter and balance the radiators and this should solve the problem.

htg
htg engineer
Posts: 3193
Joined: Tue May 22, 2007 5:22 pm


Postby Ian Thompson » Sat Jan 12, 2013 5:54 pm

Thanks htg.
Will do
Ian
Ian Thompson
Posts: 13
Joined: Thu Nov 15, 2012 2:01 pm