Central Heating switches on when the hot water is heated


Postby Tatt » Wed Jan 30, 2008 10:07 pm

Our central heating warms up when the boiler is on for the hot water - this occurs even when the central heating timer is switched off.

I've looked at the controller unit (next to the tank in the airing cupboard) when the hot water is being heated, and both the light for the central heating and the hot water lights glow.

Is it possible that the system was wired incorrectly?

The house is 4 years old.
Tatt
Posts: 2
Joined: Wed Jan 30, 2008 9:58 pm

Sponsor

Simply Build It

Postby bjbiker » Thu Jan 31, 2008 6:33 pm

It sounds like you motorised valve is defective and letting by.
Regards Bjbiker
bjbiker
Posts: 16
Joined: Mon Jan 28, 2008 4:44 pm


Postby Paulo83 » Thu Jan 31, 2008 8:04 pm

Its not 'honeywell' controls is it??
Paulo83
Posts: 23
Joined: Tue Jan 01, 2008 6:21 pm


Postby Tatt » Thu Jan 31, 2008 10:34 pm

Hi

Thanks for the replys. I have "Potterton Controls".

Tatt
Tatt
Posts: 2
Joined: Wed Jan 30, 2008 9:58 pm


Postby Kenj » Fri Feb 01, 2008 7:38 pm

Hi Guys,
Sorry to dissagree, but if the CH light is lit on the Control Unit / Programmer, then the relavent motorised valve will be turned on (Opened), if the room stat (if fitted) is also on.
This light is not a feedback signal saying that the motorised valve is open. It is informing you that the Central Heating is selected (ie on, or enabled). This light should never come on when CH is not selected on the Control Unit.
And in answer to the original question:- Yes I suspect that the unit is miswired.
Kenj
Posts: 80
Joined: Mon Jan 28, 2008 8:30 pm