central heating

by jeffrapido » Mon Nov 19, 2007 4:00 pm

Hi,

The radiator in my living room (which is furthest from system) is cold. If I closed some radiators upstairs it get warm a bit but just on top. Also I hear knocking sound behind the wall. Please help. :cry:

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Mon Nov 19, 2007 6:25 pm

Could be airlock, blockage or faulty radiator valve.

Firstly check pump setting and turn up if possible, then try removing radiator to see if there's water to both valves, if the water doesn't flow freely then there's probably a blockage in the pipe or at the manifold.

Look at other posts to see how to clear airlocks and blockages

jeffrapido
Labourer
Labourer
Posts: 2
Joined: Mon Nov 19, 2007 3:39 pm

by jeffrapido » Wed Nov 21, 2007 11:27 am

Thanks for the advise. I check my pump and its in max setting.

I think the problem is blockage. I am planning to use sludge removal solution. I am planning to drain my heating system. I have two tanks in my loft, one big with a label drinking water and a smaller one with no label, could I put the sludge removal on the smaller tank and circulate it for a few days and drain it out (and possible remove the rad with problem)and put an inhibitor after? I would greatly appreciate your advice. Many thanks