CH only comes on when DHW comes on
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

3 posts   •   Page 1 of 1
NovaNath
Labourer
Labourer
Posts: 2
Joined: Mon Sep 08, 2008 8:47 pm

CH only comes on when DHW comes on

by NovaNath » Mon Sep 08, 2008 9:09 pm

Potterton Prima F with EP2001 control.

The DHW functions as it should.

The CH thermostat was turned down for the summer; when turned up to activate the CH, the boiler will only fire if the DHW is already on/coming on at same time as the heating.
Where the hot water is not on, the boiler makes no noises at all/no response. However the CH light iluminates on the valve and it hums/clicks quietly.

Any help greatly apreciated.
(my gut instinct is that it may be the EP2001 control not telling the boiler to fire)

NovaNath
Labourer
Labourer
Posts: 2
Joined: Mon Sep 08, 2008 8:47 pm

by NovaNath » Sat Sep 13, 2008 4:21 pm

Diagnosed to the actuator on the three way valve

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Sun Sep 14, 2008 10:50 am

See looking through other questions and answers in the forum often leads to the correct diagnosis - there's been many many posts on this subject.


htg