CH only comes on when DHW comes on


Postby NovaNath » Mon Sep 08, 2008 8:09 pm

Potterton Prima F with EP2001 control.

The DHW functions as it should.

The CH thermostat was turned down for the summer; when turned up to activate the CH, the boiler will only fire if the DHW is already on/coming on at same time as the heating.
Where the hot water is not on, the boiler makes no noises at all/no response. However the CH light iluminates on the valve and it hums/clicks quietly.

Any help greatly apreciated.
(my gut instinct is that it may be the EP2001 control not telling the boiler to fire)
NovaNath
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Mon Sep 08, 2008 7:47 pm

Sponsor

Simply Build It

Postby NovaNath » Sat Sep 13, 2008 3:21 pm

Diagnosed to the actuator on the three way valve
NovaNath
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Mon Sep 08, 2008 7:47 pm

Postby htg engineer » Sun Sep 14, 2008 9:50 am

See looking through other questions and answers in the forum often leads to the correct diagnosis - there's been many many posts on this subject.


htg
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 