I have been advised to change an existing 80A/30mA RCD with a 100A/30mA RCD and run all MCB's from the latter to conform with 17th Edition Regs. Is this OK?
I am qualified electrician but now retired and not practiced for some time
edtheted
Rank: Labourer
Progress to next rank:
75%
Posts: 4
Joined: Thu Nov 18, 2010 8:39 am

Sponsor

Simply Build It

Postby ericmark » Sat Feb 05, 2011 12:29 am

As to comply with 17th Edition nothing has changed to require that change.
Depending on DNO fuse size and MCB sizes it could be under rated but unlikely it would cause a problem.

Two main changes are with certain exceptions all circuits need RCD protection.

314.1 Every installation shall be divided into circuits, as necessary, to:
(iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit.
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation.

Really that has always been the case but now spelled out. There are three ways used to comply.
Using RCBO's
Using multi (2) RCD's
Emergency lights.

With existing installations easy to know if it complies. If the RCD does not regularly trip it complies even if only one. But with new only safe way is RCBO as one has no idea what will be used.

There is no requirement to up-grade however when for example fitting new sockets to a system that does not comply it is a pain to use Ali-tube cable and RCD sockets. (Ali-tube does not need RCD protection buried T&E does)
ericmark
Rank: Project Manager
Posts: 1739
Joined: Fri Oct 02, 2009 8:49 pm
Location: Mold, North Wales.

Postby edtheted » Sat Feb 05, 2011 11:24 pm

edtheted wrote:I have been advised to change an existing 80A/30mA RCD with a 100A/30mA RCD and run all MCB's from the latter to conform with 17th Edition Regs. Is this OK?
I am qualified electrician but now retired and not practiced for some time



ericmark
Thanks the information was very helpful
edtheted
edtheted
Rank: Labourer
Progress to next rank:
75%
Posts: 4
Joined: Thu Nov 18, 2010 8:39 am

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 