combi boiler high pressure guage reading


Postby bongo » Wed Sep 03, 2008 6:14 pm

I have a baxi 105e combi boiler that is causing the pressure to rise rapidly to 3.5bar ( ie 24 hours ) whereupon the pressure relief valve operates. I let the pressure out via the relief valve to .7 bar to keep it running which it does fine. It does this if using hot water mode only or both. I've checked the expansion vessel and seems to be ok no water in it,Boiler only 4 yrs old any ideas ?
bongo
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Wed Sep 03, 2008 5:53 pm

Sponsor

Simply Build It

Postby htg engineer » Thu Sep 04, 2008 10:47 am

If the pressure vessel is ok, and the combi fill is disconnected - then it's probably the plate heat-ex causin the problems, the smallest hole in the heat-ex will allow water to enter the heating section.

htg
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Postby bongo » Thu Sep 11, 2008 6:44 pm

Thanks to htg engineer plate exchanger replaced, boiler now sorted.
bongo
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Wed Sep 03, 2008 5:53 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 