Postby dw565656 » Tue Jun 19, 2007 6:48 pm

I have recently had installed by a qualified electrician the components of a Danfoss control pack with the wiring box. My problem is with the HS 3 port valve, the plumbing bit I did myself - it does not open the valve for the heating. Hot water is ok. The supplier said the thought it was the valve and supplied a new one - same problem. Looking at the actuator when not connected to the valve showed that the spindle was not moving sufficiently. Back to the suppliers for new actuator! Same problem. The electrian has double checked all the wiring and has confirmed the correct voltage from the room stat, and we have tried a new room stat.

Any suggestions?
dw565656
Posts: 2
Joined: Tue Jun 19, 2007 6:24 pm

Sponsor

Simply Build It

Postby sparx » Wed Jun 20, 2007 8:05 pm

Hi, get your leckie to check wiring to cylinder stat. should have 3 cores plus earth connected other wise when water hot, v/v won't go to heating pos. (gets a back feed from 'satisfied' position of tank stat.
regards SPARX
sparx
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.


Postby dw565656 » Wed Jun 20, 2007 8:42 pm

Thanks for suggestion, but problem fixed today. Electrician spoke to Danfoss. It was a missing connection from the programmer, not sure of the details only know it was grey wire. main thing is it all works now. Thanks again for your time.
dw565656
Posts: 2
Joined: Tue Jun 19, 2007 6:24 pm