Disconnected Smoke Detector From Burglar Alarm now Zone has Issues

Postby Paul1212 » Thu Feb 15, 2018 3:52 pm

I have disconnected a smoke detector in my home that was wired into the burglar alarm using 4 wires because it kept going off despite the fact that there was no smoke.
I insulated all the wires that were loose and thought that would be OK, but now when I set my burglar alarm the zone that the smoke detector was connected to lights up and I have to omit this zone in order to set the alarm.

The terminals that the wires were connected to on the smoke detector were labelled: -

Can anyone tell me what I need to do to stop this from happening?

BTW I have put up some new smoke alarms to replace this one.

Many thanks in advance.
Rank: Labourer
Progress to next rank:
Posts: 1
Joined: Thu Feb 15, 2018 3:31 pm


Simply Build It

Postby Mr White » Thu Feb 15, 2018 8:30 pm

Intruder alarms work by having detection devices that go "open" when they detect. (So a burglar can not cut the wire to bypass the alarm)
Since you have removed a smoke detector you have left the circuit "open" You need to connect the two wires that were on C and NC together.
Keep the other two apart, as they will be the 12v supply.
Mr White
Rank: Ganger
Progress to next rank:
Posts: 178
Joined: Tue Jun 20, 2017 9:54 pm

Display posts from previous
Sort by
Order by

  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!


  • Related Topics