Distance between pipes and cables


Postby hamish72 » Tue Sep 15, 2009 8:20 pm

Is there anything in regs to specifi a minimum gap between mains cable run and parallel hot water pipe
hamish72
Posts: 27
Joined: Sun May 25, 2008 5:11 pm

Sponsor

Simply Build It

Postby sparx » Sun Sep 20, 2009 1:44 pm

Hi, electrical reg.528.3.1 (for the pedants who want to check) says
A wiring system shall not be installed in the vicinity of services which produce HEAT, smoke or fumes likely to be detrimental to the wiring, unless it is protected from harmful effects by shielding arranged so as not to affect the dissipation of heat from the wiring.

Our guidance book on installation suggests 50mm as minimum distance, and should never be in contact with other services.

Sorry for late answer but not often on this part of forum, normally on leckie bit,
regards Sparx
sparx
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.


Postby hamish72 » Sun Sep 20, 2009 2:12 pm

Many thanks for that I just could not find it and you answered it all very well thanks again :D