Postby JIM CAROLAN » Wed Dec 23, 2009 10:47 pm

I have an indirect central heating system,I drained the system last summer to repair a radiator. On recommissioning the system I have lukewarm hot water in all taps and no heat in one radiator. I vented the radiator and it has no effect,if the primary circuit contains air how do I vent it?
JIM CAROLAN
Rank: Labourer
Progress to next rank:
0%
Posts: 1
Joined: Wed Dec 23, 2009 10:27 pm

Sponsor

Simply Build It

Postby plumbbob » Thu Dec 24, 2009 9:49 am

Generally airlock associated with single radiators can be cleared by simply manually turning off all the other rads and switching to CH only on the timer (unless you have a combi). The increase in pressure will force the air into the rad.

There ought to be a bleed valve in the pipework near the top cylinder coil. If this does not expel the air, the only solution may be to crack open a nearby joint to allow the air to escape.
plumbbob
Rank: Project Manager
Posts: 1873
Joined: Wed May 07, 2008 9:59 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 