downstairs socket ring tripping


Postby smonks » Tue Jun 15, 2010 11:30 am

The downstairs socket MCB on my consumer unit has started tripping sporadically, leading the RCD to trip - even when absolutely everything on that ring is unplugged. We've had no electrical or building work done since 2007. Any ideas what might be causing it? Many thanks.
smonks
Posts: 1
Joined: Tue Jun 15, 2010 11:25 am

Sponsor

Simply Build It

Postby ericmark » Tue Jun 15, 2010 9:17 pm

I have had MCB's tripping when they have had some twisting moments due to have they have been tightened up in dis board and when they have been tripping due to regular overload. There is a recall on at the moment over faulty MCB's but since I have not fitted any in the qualifying period I did not make any notes.
Seem to think some of the electron range. Maybe others can confirm and give dates and make of the recall.
ericmark
Posts: 1221
Joined: Fri Oct 02, 2009 8:49 pm
Location: Mold, North Wales.


Postby beckykate » Wed Jun 16, 2010 9:06 am

It's unlikely to be related to the recall as the dates do not match.

Details of recalled items can be found here
http://www.neweysonline.co.uk/News-Elec ... ic.raction
beckykate
Posts: 4
Joined: Thu Aug 16, 2007 9:43 am


Postby sparx » Wed Jun 23, 2010 5:45 pm

you mention no building work, but think wider,
new carpet gripper strip nailed? squeeking board screwed down?.
No? time to get a leckie in to do circuit insulation test (megger check).
sparx
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.