Earth bonding at gas meter


Postby Lee the novice » Tue Apr 24, 2007 7:36 am

Hi all,

I have a contract for the house with BG. On their inspection they say the earth bonding is on the wrong side of the gas meter (it was on the pipe that went into the ground). On asking him he said it should be between the meter and the house and be within 600mm of the meter.

I bought a new earth strap and moved the original earth wire to the house side of the meter, it's before any joints and within 600mm.


Is this correct???
Lee the novice
Posts: 2
Joined: Tue Apr 24, 2007 7:31 am

Sponsor

Simply Build It

Postby Jeffmo » Tue Apr 24, 2007 7:29 pm

sounds ok , but make sure it is 10mm earth wire and make sure the contact surface of pipe to clip is clean . Also remember you shouldn't be doing it . Naughty naughty. Regards Jeff. PS get a qualified leckie to check all bonding its important to save your life
Jeffmo
Posts: 103
Joined: Mon Apr 09, 2007 9:22 am


Postby sparx » Tue Apr 24, 2007 7:49 pm

yessir as long as it's after flex pipe
sparx
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.


Postby Lee the novice » Thu Apr 26, 2007 6:09 am

Many thanks
Lee the novice
Posts: 2
Joined: Tue Apr 24, 2007 7:31 am