Postby antony5378 » Sat Mar 07, 2009 4:34 pm

This is a bit puzzling.

I'm wiring a light switch in my kitchen, when i connect the lives from the ring to the live for the light, the earth cable is also living-up.

The earth is unconnected at both ends, so the current must be transferring from the live to the earth, without actually being in contact with it, how i do not know.

Any advice would be appreciated.
antony5378
Posts: 4
Joined: Tue Oct 09, 2007 11:34 am

Sponsor

Simply Build It

Postby kbrownie » Sat Mar 07, 2009 8:58 pm

hi anthony5378,
this is not good, i'd be checking all connection at light fitting for a loose earth or a loose live that are touching. Or connection that has been terminated wrongly. also check at cu in case it has happened there If you can not find it straight away call a electrician.
KB
kbrownie
Posts: 1757
Joined: Mon Mar 05, 2007 9:36 pm


Postby sparx » Sat Mar 07, 2009 9:35 pm

Hi, £ to a pile of rat sh@t you are using one of those bl00dy neon test screw driver things!!
Dangerously misleading pieces of junk which should be banned from sale for all time IMHO.
It's called 'capacitive coupling'. If you use a proper moving coil test meter you will find it is not actually live at all. If it where, connecting it to earth wires at ceiling would blow fuse/mcb.
NB "Capacitor" two parallel conducting surfaces seperated by insulating material, (ie, just like a twin & earth cable).
regards Sparx
sparx
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.


Postby moggy1968 » Sun Mar 08, 2009 4:50 pm

The other possibility is you've lost a neutral somewhere and the earth is now providing your neutral return path. This should trip the switch, but I have seen it when it doesn't. It could be an earth neutral reversal somewhere.
Andy
moggy1968
Posts: 198
Joined: Sat Feb 21, 2009 11:32 am