    Earth Fault, Loop Test Reading >200ohms



    neweysonline.co.uk - The newest tool of the trade




    Post a reply




    19 posts • Page 1 of 2 • 1, 2

    Earth Fault, Loop Test Reading >200ohms

    Postby The Renovator » Fri Jun 15, 2007 6:05 pm

    Hi,

    I'm new to this forum and not an expert by any means.

    Scottish Gas came to do a service on my boiler today but wouldn't go near it because their electrical test revealed an "Earth Fault, Loop Test Reading >200ohms".

    I spoke to the engineer on the telephone (as I wasn't there when they visited) and he told me the reading was "around 200ohms" but should be below 1ohms.

    My question is - should I be switching off my mains switch and continuing this post on battery power until I get an electrician in or should I be okay to wait until he arrives in a few days?

    The Scottish Gas engineer did tests on several plug sockets in my house (upstairs and down) and found similar readings through out. I don't have a clue why this would be, nor do I understand why it seems to be consistent throughout the house (what with all the circuits being on different loops).

    Can anyone explain the technicalities too? e.g. if there is a fault on one circuit, should I expect it to affect the entire supply?


    Thanks in advance,

    The Renovator
    The Renovator
     
    Posts: 6
    Joined: Fri Jun 15, 2007 5:55 pm
    Top

    Re: Earth Fault, Loop Test Reading >200ohms

    Postby BLAKEY1963 » Sat Jun 16, 2007 12:19 am

    [quote="The Renovator"]Hi,

    I'm new to this forum and not an expert by any means.

    Scottish Gas came to do a service on my boiler today but wouldn't go near it because their electrical test revealed an "Earth Fault, Loop Test Reading >200ohms".

    I spoke to the engineer on the telephone (as I wasn't there when they visited) and he told me the reading was "around 200ohms" but should be below 1ohms.

    My question is - should I be switching off my mains switch and continuing this post on battery power until I get an electrician in or should I be okay to wait until he arrives in a few days?

    The Scottish Gas engineer did tests on several plug sockets in my house (upstairs and down) and found similar readings through out. I don't have a clue why this would be, nor do I understand why it seems to be consistent throughout the house (what with all the circuits being on different loops).

    Can anyone explain the technicalities too? e.g. if there is a fault on one circuit, should I expect it to affect the entire supply?


    Thanks in advance,

    The Renovator[/quote]



    THE RENOVATOR
    ARE WE ASSUMING THAT SCOTTISH GAS
    PERFORMED AN EARTH LOOP IMPEADANCE TEST AND GOT A READING
    OF 200 OMHS +.
    OK THEN IF WE ARE , THEY THEN STATED THAT THE READINGS SHOULD BE BELOW 1 OMH , IT IS POSSIBLE YOU COULD HAVE A PROBLEM WITH EARTHING.
    IF YOUR SUPPLY TO YOUR HOUSE IS A T.N.S OR T.N.C.S THEN THE
    NORMAL GUIDELINES FOR EARTH LOOP IMPEADANCES ARE

    T.N.S NOT HIGHER O.80 OMHS FOR ZE

    T.N.C.S NOT HIGHER 0.35 0MHS FOR ZE

    CHECK IMMEADIATLY WITH YOUR REGISTERED ELECTRCIAN WHAT METHOD OF EARTHING YOUR SUPPLY IS , IF T.N.S OR T.N.C.S THEN YOU
    HAVE SERIOUS EARTHING PROBLEMS WITH THE READING TAKEN ,
    SHOCK RISK COULD VERY WELL EXIST , AND THIS NEEDS TO BE ADDRESSED WITH YOUR ELECTRICIAN AS SOON AS POSSIBLE
    ISOLATION OF SUPPLY WOULD BE SENSIBLE UNTILL YOU SPEAK TO YOUR ELECTRICIAN.
    BLAKEY1963
    BLAKEY1963
     
    Posts: 655
    Joined: Wed Jun 13, 2007 10:57 pm
    Top

    Postby The Renovator » Sat Jun 16, 2007 7:59 am

    Thanks for the reply Blakey1963. To be honest with you, I don't know what type of test Scottish Gas performed but the guy did say I had an earthing problem so it looks like your response is appropriate to my problem.
    Can I ask if you or anyone else knows how such problems are typically remidied? e.g. Would it mean tearing the house apart to find a specific fault or is it just a case of installing appopriate earthing in one particular location? Reason I ask is because these high readings came from various plug sockets throughout the house.
    Please excuse my ignorance on this matter and provide answers as if I was a woman or a child! (which I could well be for the purposes of being ploitically correct!)
    The Renovator
     
    Posts: 6
    Joined: Fri Jun 15, 2007 5:55 pm
    Top

    Postby BLAKEY1963 » Sat Jun 16, 2007 9:10 am

    [quote="The Renovator"]Thanks for the reply Blakey1963. To be honest with you, I don't know what type of test Scottish Gas performed but the guy did say I had an earthing problem so it looks like your response is appropriate to my problem.
    Can I ask if you or anyone else knows how such problems are typically remidied? e.g. Would it mean tearing the house apart to find a specific fault or is it just a case of installing appopriate earthing in one particular location? Reason I ask is because these high readings came from various plug sockets throughout the house.
    Please excuse my ignorance on this matter and provide answers as if I was a woman or a child! (which I could well be for the purposes of being ploitically correct!)[/quote]

    THE RENOVATER
    IF YOUR PROBLEM,( AND OBVIOUSLY THIS IS IF,)
    IS THAT YOU HAVE A MEANS OF EARTHING PROVIDED BY YOUR REGIONAL ELECTRCITY SUPPLIER AND ITS VALUE IS BELOW 1 OMH,
    THEN YOUR ELECTRCIAN WOULD CHECK FOR CORRECT CONNECTION
    OF AN EARTHING CONDUCTOR TO THIS PROVIDED POINT OF EARTHING,
    KNOWN AS THE MAIN EARTH TERMINAL.
    THIS EARTHING CONDUCTOR FROM THE MAIN EARTHING TERMINAL
    GOES TO YOUR EARTHING TERMINAL AT THE CONSUMER UNIT.
    ONCE THE EARTH LOOP AT THIS POINT CAN BE TESTED AT LESS THAN
    1 OMH ( AS SCOTTY GAS IS TELLING U ) . THE VARIOUS C.P.C.S
    FOR YOUR INDIVIDUAL CIRCUITS ( THE BARE COPPER WIRES WITHIN THE TWO CORE CIRCUIT CABLES, WHICH HAVE GREEN AND YELLOW EARTH SLEEVEING ON ) NEED TO BE CONNECTED TO THIS EARTHING
    TERMINAL.
    SO THEN AS LONG AS ALL THESE CONNECTIONS ARE COMPLETE AND SOUND .THEN YOUR EARTH LOOP IMPEADANCE READINGS SHOULD
    BE ACCEPTABLE DEPENDING ON EXTERNAL EARTH LOOP IMPEADANCE
    AND IMPEADANCES FROM CIRCUIT CABLES ( R1 +R2 )
    EARTH READINGS SUITABLE FOR TYPE OF PROTECTIVE DEVICE (MCB)
    THE ONLY TIME THAT TOTAL DISRUPTION COULD BE POSSIBLE IS IF YOUR ELECTRICIAN IS TO OBTAIN TEST RESULTS OF UNSATISFACTORY CONTINUITY , INSULATION , OR EARTH LOOP IMPEADANCE READINGS FROM ANY OF YOUR CIRCUIT CABLES.
    IT COULD BE A CASE FOR REPLACEMENT OF ANY FAULTY CABLES
    BY REWIRING.
    MY ADVICE, DO NOT DELAY, PLEASE CONTACT YOUR ELECTRCIAN
    IMMEADIATLY. EARTHING PROMLEMS HAVE BEEN QUOTED AND A POSSIBLE SHOCK RISK EXISTS AND IN SOME CASES FIRE.

    GET IT CHECKED ASAP

    BLAKEY1963
    BLAKEY1963
     
    Posts: 655
    Joined: Wed Jun 13, 2007 10:57 pm
    Top

    Postby BLAKEY1963 » Sat Jun 16, 2007 5:09 pm

    [quote="The Renovator"]Thanks for the reply Blakey1963. To be honest with you, I don't know what type of test Scottish Gas performed but the guy did say I had an earthing problem so it looks like your response is appropriate to my problem.
    Can I ask if you or anyone else knows how such problems are typically remidied? e.g. Would it mean tearing the house apart to find a specific fault or is it just a case of installing appopriate earthing in one particular location? Reason I ask is because these high readings came from various plug sockets throughout the house.
    Please excuse my ignorance on this matter and provide answers as if I was a woman or a child! (which I could well be for the purposes of being ploitically correct!)[/quote]

    RENOVATOR SENT U PREVIOUS RESPONSE TO ABOVE BUT DO NOT THINK U RECIEVED IT.
    IF U HAVE NOT CONTACTED YOUR ELECTRCIAN YET YOU MUST DO SO
    NOW !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
    HE OR YOUR ELECTRCITY SUPPLIER CAN TELL YOU THE METHOD OF EARTHING FOR YOUR INCOMING SUPPLY.
    IF IT IS ESTABLISHED THAT EARTH LOOP IMPEADANCES ARE BELOW 1 OMH AT YOUR MAINS BOARD POSITION, THEN YOUR EARTHING IS
    OKAY TO CONSIDER THE FUNCTIONING OF YOUR PROTECTIVE DEVICES. ( M.C.B. S / FUSES )
    WITH A VALUE OF EARTH LOOP IMPEADANCE BELOW 1 OMH, IT WOULD JUST BE A MATTER OF YOUR REGISTERED ELECTRCIAN, PERFORMING
    TESTS ON YOUR CIRCUITS TO PROVE THE EARTH PATH CONTINOUS
    BACK TO YOUR MAINS BOARD.
    HE COULD ALSO REPORT TO THE BOARD IF EXTERNAL EARTH LOOP IMPEADANCES
    WERE TOO HIGH, AS SAID PREVIOUSLY TNS = 0.8 OMH , TNCS = 0.35 OMH.
    AT THE MOMENT A SHOCK AND FIRE HAZARD COULD BE PRESENT.
    GET YOUR SPARKY IN PRONTO
    BLAKEY1963
    .
    BLAKEY1963
     
    Posts: 655
    Joined: Wed Jun 13, 2007 10:57 pm
    Top

    Postby sparx » Sat Jun 16, 2007 11:11 pm

    Hi further to 'Blakeys' valid comments; for information.
    there are 2 main types/methods of earthing an installation, one - going out of favour now, is to use an earth rod outside, connected to your installation, which would require an RCD for protection.(T T) The rod giving a reading typically of a few ohms up to a few hundred ohms depending upon soil type, (on chalk hills locally 60-75 ohms usual).
    On older (circa 1960's) installation there may be a Voltage operated trip, identifiable by having 2 earth wires connected to it, not valid any longer as unreliable/untestable.
    The other system is a variation of earths provided by supply company, either from cable sheath (TN-S) or from term on side of fused 'cut-out'
    (TN-C-S) also called PME. These give the readings approx as suggested.
    A visual check at the intake meter position will confirm which you have.
    If TT (rod) & RCD is fitted all may be well, but don't delay in finding out,
    without wishing to deride the original observation of the gas man he may not be familiar with TT readings, get a good local sparky to look-soon!
    regards SPARX
    sparx
     
    Posts: 2166
    Joined: Wed Mar 21, 2007 8:33 pm
    Location: The fifth continent.
    Top

    Postby The Renovator » Sun Jun 17, 2007 11:38 am

    Thanks for the replies guys. Quite technical for me to understand but the over-riding theme is understood.

    Can anyone tell me what institutions a competent Sparky should be registered with or where I can find a list that tells me which electricians in my area are affiliated with the right associations etc?
    The Renovator
     
    Posts: 6
    Joined: Fri Jun 15, 2007 5:55 pm
    Top

    Postby sparx » Sun Jun 17, 2007 6:01 pm

    Hi agn,
    we are registered with the 'Electrical Contractors Association' (E.C.A), & for our domestic 'Part P' & other routine Inspections & testing services we are members of National Association of Professional Inspectors & Testers
    (N.A.P.I.T).
    There is also The National Inspection Council for the Electrical Industries Contractors, (NICEIC).
    All the above have adverts in the telephone local directories & web sites; all list approved members by area/post code etc.
    For domestic work you need to look for the 'Domestic Installer' logo, rather than just 'member of...'
    Now also the Government backed 'Trust Mark' scheme gives insurence backed guarentees for companies who sign up to the scheme so if unsatisfactory work done it will be put right at no cost to customer.
    Avoid unmarked vans with only mobile number!
    regards SPARX
    sparx
     
    Posts: 2166
    Joined: Wed Mar 21, 2007 8:33 pm
    Location: The fifth continent.
    Top

    Postby BLAKEY1963 » Sun Jun 17, 2007 8:28 pm

    [quote="The Renovator"]Thanks for the replies guys. Quite technical for me to understand but the over-riding theme is understood.

    Can anyone tell me what institutions a competent Sparky should be registered with or where I can find a list that tells me which electricians in my area are affiliated with the right associations etc?[/quote]

    THE RENOVATOR
    SPARX HAS GIVEN ACCURRATE , PRECISE INFOMATION , SO I AM SURE HIS WORDS OF ADVICE ARE WELL NOTED,
    AND YOU WILL ACT ON THEM.
    MYSLEF JUST TO ADD AM A DOMESTIC INSTALLER, CURRENTLY GOING
    THROUGH REGISTRATION WITH N.I.C.E.I.C . YOUR LOCAL TRADING STANDARDS CAN HELP , CLARIFY APPROVED CONTRACTERS.
    WE AS DOMESTIC INSTALLERS WITH N.I.C.E.I.C ARE TOLD TO ISSUE
    CUSTOMER WARRENTIES FOR ALL WORK DONE, AND CONFIRM WITH THE CUSTOMER IN WRITING WHAT IS TO BE CARRIED OUT, AND SIGNED BY THEM, AND THE FINISHED BILL SHOWS THIS WORK CARRIED OUT,
    TOGETHER WITH TEST CERTIFICATES , CIRCUIT SCHEDULES, WIRING
    ROUTES, AND OTHER INSTALLATION INFORMATION.
    ROUTES. AS I SAID RENOVATOR PLEASE GET YOUR INSTALLATION
    CHECKED OUT IMMEADIATELY.
    I WOULD LIKE TO THANK SPARX FOR HIS INPUT ON THE RENOVATOR,S
    INQUIRY.
    THANK YOU SPARX ! BLAKEY1963
    BLAKEY1963
     
    Posts: 655
    Joined: Wed Jun 13, 2007 10:57 pm
    Top

    Postby sparx » Mon Jun 18, 2007 10:06 pm

    Thanks Blakey , Didn't want to 'horn-in' but feel when someone is trying to do things right they deserve as much help/info as poss. best wishes both,
    SPARX
    sparx
     
    Posts: 2166
    Joined: Wed Mar 21, 2007 8:33 pm
    Location: The fifth continent.
    Top

    Postby BLAKEY1963 » Mon Jun 18, 2007 11:57 pm

    [quote="sparx"]Thanks Blakey , Didn't want to 'horn-in' but feel when someone is trying to do things right they deserve as much help/info as poss. best wishes both,
    SPARX[/quote]

    SPARX
    YOU ARE NOT HORNING IN, PLEASE FEEL FREE TO ADVISE ME IF YOU
    CAN , I HAVE READ YOUR INPUT ON THIS SITE OVER THE LAST TWO
    MONTHS OR SO AND YOU ARE AN INCREDIBLE MAN OF MUCH
    ELECTRICAL EXPERIENCE , AND I THINK WE ARE VERY VERY LUCKY
    THAT YOU ARE WILLING TO SHARE YOUR KNOWLEDGE ON THIS SITE.
    THERE ARE A LOT OF GRATEFUL PEOPLE ON THIS SITE WHO YOU HAVE
    GUIDED, MYSLEF ONE OF THEM.
    I WANT TO THANK YOU THE SHORT TIME I HAVE BEEN ON THIS SITE
    FOR YOUR HELP AND ADVICE AND LOOK FORWARD TO YOUR
    VALUEBLE CONTRIBUTIONS.
    ONCE AGAIN THANK YOU SPARX !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!

    BLAKEY1963
    BLAKEY1963
     
    Posts: 655
    Joined: Wed Jun 13, 2007 10:57 pm
    Top

    Postby The Renovator » Tue Jun 19, 2007 9:17 pm

    You guys are both doing a fine job - great that you are willing to offer this advice for free.
    To update you, I had a sparky in tonight who specialises in the testing side of things.
    The problem lies with my main supply provided by Scottish Power. It enters my house via a live and neutral feed and there is no earth present. My (recently installed) domestic wiring seems to be sound but the main supply is estimated at 60 years old, which ties in with the history of the house (which has been family owned since 1980).
    The reading on the plug sockets tonight was 626 ohms and the sparky informed me that this would have been the case before my re-wire.
    Will give Scottish Power a bell tomorrow so that this one can be dealt with ASAP.
    Anyone know if they will charge?
    Anyway, thanks again guys, good to see theres still a bit of passion around when it comes to keeping people (and their families) safe.
    The Renovator
     
    Posts: 6
    Joined: Fri Jun 15, 2007 5:55 pm
    Top

    Postby BLAKEY1963 » Tue Jun 19, 2007 10:38 pm

    [quote="The Renovator"]You guys are both doing a fine job - great that you are willing to offer this advice for free.
    To update you, I had a sparky in tonight who specialises in the testing side of things.
    The problem lies with my main supply provided by Scottish Power. It enters my house via a live and neutral feed and there is no earth present. My (recently installed) domestic wiring seems to be sound but the main supply is estimated at 60 years old, which ties in with the history of the house (which has been family owned since 1980).
    The reading on the plug sockets tonight was 626 ohms and the sparky informed me that this would have been the case before my re-wire.
    Will give Scottish Power a bell tomorrow so that this one can be dealt with ASAP.
    Anyone know if they will charge?
    Anyway, thanks again guys, good to see theres still a bit of passion around when it comes to keeping people (and their families) safe.[/quote]

    THE RENOVATOR
    GOOD NEWS YOU GOT A SPARK IN .
    JUST ASK SCOTTISH POWER IF YOUR SUPPLY THEY HAVE GIVEN U
    IS ONE THAT INCLUDES AN EARTHING FACILITY , I.E T.N.S OR T.N.C.S . ( THEY WILL TRY AND CORRECT IT SHOULD IT NOT BE PRESENT ) . IF THEY DO NOT PROVIDE AN EARTHING FACILITY THEN
    YOUR SUPPLY IS WHAT IS KNOWN AS T.T SYSTEM.
    SCOTTISH POWER SHOULD NOT CHARGE U FOR CLARIFYING THE METHOD OF EARTHING ON YOUR SUPPLY , AND IF THERE IS ONE PROVIDED BY THEM, THEY ARE RESPONSIBLE FOR GETTING IT TO A CERTAIN VALUE.
    LASTLY IF YOUR SUPPLY IS A T.T SYSTEM , THEN YOUR SPARKY WILL HAVE TO PROVIDE U WITH A METHOD OF EARTHING, NORMALY AN EARTH
    ELECTRODE ( EARTH ROD ) AND FIT R.C.D . PROTECTION ON YOUR MAINS BOARD . YOUR 16 MM2 EARTHING CONDUCTOR WOULD COME FROM THE EARTH ROD TO THE EARTH TERMINAL ON YOUR MAINS BOARD.
    LET US KNOW WHAT METHOD OF EARTHING THE BOARD SAY U HAVE.
    BLAKEY1963
    P.S IF YOU ARE LEFT WITH A TT SYSTEM WHERE YOUR EARTH LOOP
    IMPEADANCE IS FOR EXAMPLE HIGH AS IT IS NOW 600 OMHS + THEN
    YOUR SPARK WILL ADVISE ABOUT THE BEST WAY TO PROVIDE R.C.D
    PROTECTION FOR ALL CIRCUITS.
    BLAKEY1963
     
    Posts: 655
    Joined: Wed Jun 13, 2007 10:57 pm
    Top

    Postby BLAKEY1963 » Tue Jun 19, 2007 10:41 pm

    [quote="The Renovator"]You guys are both doing a fine job - great that you are willing to offer this advice for free.
    To update you, I had a sparky in tonight who specialises in the testing side of things.
    The problem lies with my main supply provided by Scottish Power. It enters my house via a live and neutral feed and there is no earth present. My (recently installed) domestic wiring seems to be sound but the main supply is estimated at 60 years old, which ties in with the history of the house (which has been family owned since 1980).
    The reading on the plug sockets tonight was 626 ohms and the sparky informed me that this would have been the case before my re-wire.
    Will give Scottish Power a bell tomorrow so that this one can be dealt with ASAP.
    Anyone know if they will charge?
    Anyway, thanks again guys, good to see theres still a bit of passion around when it comes to keeping people (and their families) safe.[/quote]

    RENOVATOR
    U COULD COULD ASK THE LIKLEHOOD OF THEM
    GROUNDING THE NEUTRALS WITH THIER SUPPLY TO GIVE T . N . C . S
    IF A T.T SUPPLY .
    BLAKEY1963
    BLAKEY1963
     
    Posts: 655
    Joined: Wed Jun 13, 2007 10:57 pm
    Top

    Postby The Renovator » Wed Jun 20, 2007 11:54 am

    Scottish Power are coming out tonight. By the sounds of it they will just do what ever is necessary to get the reading to what it should be.

    I asked the sparky who fitted originally the board about R.C.D . PROTECTION and he said he left it out because I have an old house and in such circumstances fitting R.C.D tends to make things trip all the time! Are you saying, however, that if I get my current problem sorted out then R.C.D protection won't be necessary?
    If it is necessary then is it just an upgrade to the fuse box or does it entail upgrading every socket in the house (excuse my ignorance again).
    The Renovator
     
    Posts: 6
    Joined: Fri Jun 15, 2007 5:55 pm
    Top

    Next

    Post a reply

    19 posts • Page 1 of 2 • 1, 2

    Return to Electrics





     


    • { RELATED_TOPICS }
      Replies
      Views
      Last post
    • earth loop reading
      by ian2799 » Tue Jul 01, 2008 6:13 pm
      2 Replies
      1392 Views
      Last post by ian2799 View the latest post
      Wed Jul 02, 2008 5:13 pm
    • earth fault loop impedance
      by skin » Thu Aug 09, 2007 12:45 am
      2 Replies
      2455 Views
      Last post by skin View the latest post
      Thu Aug 09, 2007 4:41 pm
    • Sparky would not test circuit, CU fault.
      by LAB » Tue Oct 30, 2012 9:31 pm
      2 Replies
      186 Views
      Last post by LAB View the latest post
      Sat Nov 03, 2012 11:03 am
    • how do i test for earth ?
      by andy-10 » Mon Nov 05, 2007 2:28 pm
      4 Replies
      1496 Views
      Last post by andy-10 View the latest post
      Wed Nov 07, 2007 2:44 pm
    • external earth loop impedence to high
      by danny001 » Sat Jun 07, 2008 7:56 am
      8 Replies
      3397 Views
      Last post by ericmark View the latest post
      Sun Jun 08, 2008 9:05 pm

    • Board index
    • The team • Delete all board cookies • All times are UTC
    • SitemapIndex SitemapIndex
    • RSS Feed RSS Feed
    • Channel list Channel list
    Powered by phpBB® Forum Software © phpBB Group





    Diy Doctor Ltd  (Company No. 5863375)

    DIY  |  DIY How To  |  DIY Forum  |  Terms & Conditions  |  Privacy Policy  |  Cookie Info  

    © Copyright DIY Doctor Ltd 2011  Developed by Boson Media  Hosted by Rackspace