Earthing Circuits

Postby kevinsum » Sat Jun 02, 2007 3:34 pm

We have installed a new consumer unit and the electrician has identified there is no earth on some circuits. I'm a little concerned about this as it does not sound right. Can anyone advise on this topic ?.
Rank: Labourer
Progress to next rank:
Posts: 1
Joined: Sat Jun 02, 2007 3:30 pm


Simply Build It

Postby sparx » Sat Jun 02, 2007 8:48 pm

Hi if only lighting circuit then regs say ;
as long as noted on the test sheets issued when con. unit changed, provided no metal fittings used on the circuits then OK.
If power circuits in metal conduits then as long as conduits properly earthed at con unit & fly leads bought from metal back boxes to each fitting , agn OK if bond test carried out at each fitting,to prove earth good,
regards SPARX
Rank: Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

Display posts from previous
Sort by
Order by

  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!