En Suite Electrics


Postby billobach181 » Mon Nov 30, 2009 5:09 pm

We an en-suite shower room and toilet. The shower is a Digital Pumped shower of a 6amp spur and tied back to an MCB at the consumer unit. My question is this:- Can I take a spur off the Bedroom Ring Main through an isolating switch and then to a 6 amp RCD/RCBO unit located in the cupboard outside the en suite for the Pump and Light. Light in the shower is Low Voltage. All the en-suite fittings are totally bonded.
The reason for doing this is because its a long torturous route back to the CU.
Regards
Bill Howells
billobach181
Rank: Ganger
Progress to next rank:
25.3%
Posts: 88
Joined: Sun Mar 04, 2007 11:23 am

Sponsor

Simply Build It

Postby moggy1968 » Mon Nov 30, 2009 10:31 pm

After a fashion yes, this is the usual way I wire a shower pump. be aware though that the cable, if burried in the wall, must be protected for the whole of the new length, so your fused spur either needs to be next to the socket it feedsfrom or you must run the cable in trunking.
Your main problemis that this work is notifiable under part P regulations as the ensuite is classed as a special location
moggy1968
Rank: Ganger
Progress to next rank:
98.7%
Posts: 198
Joined: Sat Feb 21, 2009 11:32 am

Postby billobach181 » Tue Dec 01, 2009 11:32 pm

Many thanks moggy.
Bill Howells
billobach181
Rank: Ganger
Progress to next rank:
25.3%
Posts: 88
Joined: Sun Mar 04, 2007 11:23 am

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 