FAULT CODE ON WB GREENSTAR 30CDI BOILER


Postby ARTHUR1 » Fri Jan 08, 2010 3:26 pm

I have a Worc Bos Greenstar 30 CDI combi boiler. I have problems with an external condensate pipe that regularly freezes. When this happens the fault code that comes up is; AE. Can anyone please tell me what this refers to? I need to lag the condensate pipe but wanted to make sure the fault code didn't refer to anything else.
Thank you
ARTHUR1
Posts: 1
Joined: Fri Jan 08, 2010 3:14 pm

Sponsor

Simply Build It

Postby ashton » Sat Jan 09, 2010 10:40 am

We have had the same problem with this boiler and it packs up in very cold weather. It happened last year and this in the very cold weather we are having now.

How do we deal with htis problem - the plumber who fitted it clearly did not fix the problem last year
ashton
Posts: 1
Joined: Sat Jan 09, 2010 10:37 am


Postby NeilMar » Sat Jan 23, 2010 12:30 am

Your condensate pipe should when externally ran no less the 1 1/4 inchs in diameter. This should be as short as possible and as vertical as possible, with a fall no less that 5 cms per meter. With the recent big freeze even with heavily lagged pipes, they can still freeze, the ones that never ran straight down to a drain.
NeilMar
Posts: 6
Joined: Fri Jan 22, 2010 11:59 pm


Display posts from previous
Sort by
Order by


 


  • Related Topics