Looking to add one of those pop up power sockets to our island in the kitchen.

The only power going to the island is the supply to our induction hob, can we take a feed off this?

We have a concrete floor with laminate laid ontop so this is the only option other than ripping up the floor which is a no go.

Thanks in advance

kbrownie
Project Manager
Project Manager
Posts: 1995
Joined: Mon Mar 05, 2007 9:36 pm

Re: Feed off Induction Hob for Popup Power Sockets?

Post by kbrownie » Thu Jan 05, 2017 5:42 pm

No, the hob circuit should be a dedicated circuit not to be extended to sockets.

ericmark
Project Manager
Project Manager
Posts: 2852
Joined: Fri Oct 02, 2009 8:49 pm
Location: Llanfair Caereinion, Mid Wales.

Re: Feed off Induction Hob for Popup Power Sockets?

Post by ericmark » Thu Jan 12, 2017 5:52 pm

You can't feed ovens, immersion heaters, etc from a final ring, but that is to stop overload need the consumer unit. You are looking to do reverse, and what you would need to do is look carefully at the loading. And what MCB's or fuses or RCBO's are fitted.

So with a 10mm feed cable from a 45A MCB for example you would need to fit a mini consumer unit in the island so each item could not use excessive power.

With a 2.5mm feed from a 16A MCB then it will already be at it's limit.

Between the two you have to work out loading and safely limits. It may be possible, but there is no 100% answer until one knows exactly what the circuit is.