Fitting new socket plate

Postby the2ems » Thu Jan 12, 2012 10:53 am

When fitting a new socket plate to a metal wall box, should I connect the earth from the back of the plate to the earth screw on the box?
Rank: Ganger
Progress to next rank:
Posts: 54
Joined: Wed Apr 11, 2007 6:46 pm


Simply Build It

Postby ericmark » Fri Jan 13, 2012 10:46 am

I have seen electricians argue over this. Some feel the two 3.5mm brass screws are ample and there is no need for extra earth wire others point out that until the item is removed one does not know if socket faulty or no power so back box should be earthed with small bit of cable.
It does get heated at times but unless to earth the back box means there are far too many cables going into the earth connection then I see no reason not to connect.
Rank: Project Manager
Posts: 1431
Joined: Fri Oct 02, 2009 8:49 pm
Location: Mold, North Wales.

Display posts from previous
Sort by
Order by

  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!