fused spur protected radial circuit from a ring main


Postby cloggy » Thu Jul 30, 2009 7:45 pm

Is it Ok to run a 3 metre long 2.5TE cabled spur from a ring main to a 13A fused spur / switched fused spur and then run a short (1 metre max)radial circuit for two twin sockets from that fused spur. The purpose is to provide power in a loft to supply two extractor fans and a 'power' shower (hot and cold water fed not electrically heated) designed to run on a 5 amp circuit.

Regards Alan
cloggy
Posts: 3
Joined: Thu Jul 30, 2009 4:10 pm

Sponsor

Simply Build It

Postby sparx » Fri Jul 31, 2009 7:10 am

Yes!
sparx
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.


Postby moggy1968 » Tue Aug 04, 2009 12:17 am

be aware though of the requirements for RCDs on these circuits. If your current socket circuit isn't RCD protected then use an RCD protected fused spur unit.
moggy1968
Posts: 198
Joined: Sat Feb 21, 2009 11:32 am