Heating Cuts Out - Then Restarts

by Twix » Thu Oct 02, 2008 3:58 pm

Hope somebody can help please

I've been going around in circles with this problem.

I have a Protherm 80e Combi Boiler with the following problems which I don't know if they are related or not.

1: When the heating is switched on the boiler ignites ok, heats up until I get a reading of 42 on the display and then cuts out. It then comes back on automatically when the reading hits 28 and so on... The result of this is that none of the 7 rads get very warm so it's not worth keeping the heating on. Sometimes I get an error message saying FO which according to the manual means

Flow rate sensor failure, loss of system water, air lock in boiler or pump failure.
I have checked the pump is spinning by looking that the end of the spindle after removing the bleed screw. Looks ok. Is it possible it could sill be damaged and need replacing.

2: Although I had heating problems the hot water worked fine until two weeks ago. Now it goes hot and cold. To get it working I have to turn on the heating to get the pump running, then turn on the hot tap and eventually the boiler will ignite. Sometimes the water will stay hot, others it goes hot and cold.

I've had a corgi engineer out from e-On. He didn't fill me with much confidence. He had to call the manufacturer, gave them various readings which he took using various meters. Apparently these seemed ok.

He thought it could be the Pump, Diverter Valve or Flow Rate Senor causing the problem but wasn't sure if it would work even if he replaced all these. He looked puzzeled by the boiler and relyed a lot on the manual. In the end he just said what the manual said might be wrong. He said he would order the part's but never got back to me.

My question is could I need a new pump if I can see the one I have is spinning. Also would this be the likely cause of the boiler cutting out when it reaches a certain temperature.

Things I have done to date.

Replaced the Thermistor, cleaned the heat exchanger, flushed all the rads using a cleaner and water via the filling loop?

Anyone got any suggestions

screech
Ganger
Ganger
Posts: 56
Joined: Tue Sep 02, 2008 10:51 pm

by screech » Fri Oct 03, 2008 12:45 am

i'd say a restriction in the boiler, possibly pump but more than likely a blockage in the pipework inside the boiler. not that easy to diagnose when just reading a description on the net.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Fri Oct 03, 2008 9:40 am

It does sound like a faulty sensor, have both been changed CH and DHW ?

It could still be the pump though, removing and checking the impeller is the easiest way to tell.

Does the pipework feel hot ? heat only getting a few metres from boiler ? if so then it probably is the pump at fault.


htg

Twix
Labourer
Labourer
Posts: 2
Joined: Thu Oct 02, 2008 3:20 pm

by Twix » Fri Oct 03, 2008 10:37 am

I've changed what the user manual refers to as the CH Temperature Sensor on one page and Thermistor on another. I noticed one of the electrical connections was lose on it.

I haven't replaced the DHW thermistor

I haven't replaced the overheat thermostat / high limit thermostat.

I have taken the pump apart. The impeller was stuck but I managed to free it up. When doing it I heard a pop sound. Seems to be turning freely now although I did notice a little resistance on and off. When running it does make strange sounds like it's now and again. Other times it hums very quite.

When I can get the CH running the heating flow pipe between the heat exchanger and pump does get hot but as you say the pipes a few meters away are only slightly warm at best

This is probably a stupid question but does the DHW rely on the pump or could this be an unrelated problem??

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Fri Oct 03, 2008 9:25 pm

The pump will run when the hot water is on.

I would replace the pump, as it was stuck and probably is on it's way out. As you have said the water doesn't seem to get that far from the boiler - points to the pump not working correctly.


htg