hot water but no rads


Postby stephenj » Thu Jan 01, 2009 9:56 pm

hot water heats up fine but no heating. have replaced hallway thermostat and the pump. i am able to get the rads warm by manually moving the threeway valve lever. i have also replaced threeway valve motor but to no avail. with heating selected the hall thermostat will click when adjusted but the pump and valve do nothing.
please help as its getting very cold.
thanks :(
stephenj
Posts: 3
Joined: Thu Jan 01, 2009 9:43 pm

Sponsor

Simply Build It

Postby plumbbob » Thu Jan 01, 2009 11:55 pm

You don't mention a time clock. Either this is faulty or you have a problem with the wiring. Really you need an electrical tester to help identify the problem rather than just stabbing in the dark by replacing parts.

Give more information about type of system. What type of programmer? Type of hall stat? Cylinder stat? Make of TPV?
plumbbob
Posts: 1858
Joined: Wed May 07, 2008 9:59 pm


Postby Steve the gas » Fri Jan 02, 2009 7:08 am

Hi Stephen,

Time for a drain down + replace 3 port valve body IMO.

Hth
Steve the gas
Posts: 780
Joined: Sun May 04, 2008 7:07 am


Postby stephenj » Fri Jan 02, 2009 11:30 am

[quote="plumbbob"]You don't mention a time clock. Either this is faulty or you have a problem with the wiring. Really you need an electrical tester to help identify the problem rather than just stabbing in the dark by replacing parts.

Give more information about type of system. What type of programmer? Type of hall stat? Cylinder stat? Make of TPV?[/quote]

programer=acl lifestyle lp241
hallstat=drayton rts1
mpv=acl lifestyle 679h340-3olo
cylinder stat=acl hts2
stephenj
Posts: 3
Joined: Thu Jan 01, 2009 9:43 pm


Postby stephenj » Fri Jan 02, 2009 9:11 pm

[quote="Steve the gas"]Hi Stephen,

Time for a drain down + replace 3 port valve body IMO.

thanks for your advise,all working fine now.

thanks again
steve
stephenj
Posts: 3
Joined: Thu Jan 01, 2009 9:43 pm