Bought a thermostat for a combi boiler and can't work out how to wire it in. The thermostat is 230v, the instrusctions say 230v input and output, and has terminal connectors for N L SL. The boiler has 2 connections for a thermostat that currently just has a bit of cable connected between them meaning the heating is permanently on unless switched off manually. the voltage between the 2 connectors in the boiler however is only 12v. does this mean that the thermostat is incompatible with the boiler? If not how should it be wired?
rosebery
Project Manager
Posts:
2021
Joined: Wed Sep 26, 2007 8:55 pm
Post by rosebery »
Fri Dec 04, 2009 7:07 pm
Ollie
It would be a good plan to identify what it is that you a trying to connect to what by reference to manufacturer and model / part number rather than a generic "boiler" and "thermostat".
Cheers
DEEARR2
Ganger
Posts:
160
Joined: Sun Oct 12, 2008 8:49 pm
Post by DEEARR2 »
Fri Dec 04, 2009 8:23 pm
If you have a standard mechanical type thermostat then connect across L & SL. The N connection is there to operate an anticipator that closes the on/off differential by a couple of degrees.