Melted Connector Block In Shower
Ask questions and find answers to many subjects relating to electrics and electrical work

4 posts   •   Page 1 of 1
wingwah
Labourer
Labourer
Posts: 2
Joined: Tue Sep 29, 2009 10:32 am

Melted Connector Block In Shower

Post by wingwah » Tue Sep 29, 2009 10:46 am

Hi there. The connector block in my shower has melted (smoking and wires also melted) on the neutral side, i have had the shower approx 6 months and had no problems until now. there doesnt appear any evidence of water getting in to the unit and no bare wires touching. anyone any ideas as to what it could be and should i just replace the connector block?

www.predictthescore.me.uk/shower.jpg for an image of the shower



thanks for any help[/img]
Last edited by wingwah on Wed Sep 30, 2009 12:41 pm, edited 1 time in total.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

Post by sparx » Tue Sep 29, 2009 4:13 pm

terminal not fully tightened, should be retightened after a few uses of shower as often found to become loose and will then arc,
most burnouts start with loose connections,
regards Sparx

wingwah
Labourer
Labourer
Posts: 2
Joined: Tue Sep 29, 2009 10:32 am

Post by wingwah » Tue Sep 29, 2009 11:14 pm

so if i replace the connector block with a new one and make sure all the connections are tightened will this be ok to use or do i need to get an electrician out.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

Post by sparx » Wed Sep 30, 2009 9:43 pm

probably thats all leckie would do, but if one is loose what about the others ie in local isolator switch and at consumer unit?
An electric shower is the highest single load in most homes, worth getting it checked I would say,
regards SPARX

4 posts   •   Page 1 of 1