    new cooker tripping main rcb



    Post a reply




    11 posts • Page 1 of 1

    Postby basey » Sat May 19, 2007 12:16 pm

    I have just had a 900mm range cooker delivered it is a single oven and gas hob. when plugged in through a 30amp cooker socket it recieves electric as lights etc work but as soon as the oven is turned on it trips the main house circuit breaker (not the cooker supply rcb). when testing the socket it runs a kettle or other item no problem. I have an engineer on monday from smeg to check the new oven but is it something wrong with my supply/earthing ?
    basey
     
    Posts: 2
    Joined: Sat May 19, 2007 12:10 pm
    Top

    Sponsor

    Neweys - The newest tool of the trade

    Postby Jeffmo » Sat May 19, 2007 5:44 pm

    Hi sounds to me like it could be your cable sizing , check the cooker output and get back to the forum also see what size the cable from switch to fuse box / consumer unit is .Regards Jeff
    Jeffmo
     
    Posts: 103
    Joined: Mon Apr 09, 2007 9:22 am
    Top

    Postby sparx » Sat May 19, 2007 7:41 pm

    Hi, as circuit mcb does not trip but apparently the main RCD trips then indicates an earth fault on oven, was flex/ plug already connected to oven ie moulded on plug or has it been fitted there? Anyway as light works ok it points to either damp in oven element or loose connection on oven, don't think house supply at fault, regards SPARX
    sparx
     
    Posts: 2166
    Joined: Wed Mar 21, 2007 8:33 pm
    Location: The fifth continent.
    Top

    Postby basey » Tue May 22, 2007 8:52 pm

    thanks sparx the engineer attended and after 1/2 hour found a frayed wire which was touching the cooker body. shows my earth trip was working well ! Not sure how it got frayed in a brand new cooker but still easily fixed.
    basey
     
    Posts: 2
    Joined: Sat May 19, 2007 12:10 pm
    Top

    Postby Obbzi » Thu May 24, 2007 8:14 am

    I am having a similair problem :cry: Just had a new kitchen fitted with a double oven, when we turned the smaller oven on fine, when we turned main oven on, oven switch tripped out in fuse box , reset the trip and had both ovens running together fine. Tried to turn the main oven on the other day and it tripped the oven switch in the fuse box again and it can't be reset :cry:

    Kitchen fitter installed 10mm cable from oven to oven isolation switch in kitchen and the mains box has a 30amp trip thing.

    Any ideas? :cry: :cry:
    Obbzi
     
    Posts: 1
    Joined: Thu May 24, 2007 8:10 am
    Top

    Postby pdenni » Thu May 24, 2007 7:02 pm

    hi obbzi

    30 amp breaker seems a little too small for that oven if you have the instructions tell me what the kw rating of the oven is and i will work it out for you
    pdenni
     
    Posts: 15
    Joined: Thu May 24, 2007 6:43 pm
    Top

    Postby Jeffmo » Thu May 24, 2007 8:42 pm

    cookers are usually protected by a 30 amp fuse or mcb for a cooker rated at up to 12kw and a 45 amp fuse or 50 amp mcb is needed for a cooker rated at above 12kw.So initially check the rating of the cooker , i am a bit suspicious about the fuse rating , reason being 30 amp really only needs 6mm cable up to 20 metres and 10mm cable if the run is between 20 and 30 m , i have a feeling that the protection is too small . Another possible is inside the cooker connection box or cooker switch there is a loose connection . If the switch incorporates a 13amp socket opening then they are notorious for loose conns , due to the amount of cable chucked in the back of them , especially with the larger cables from 10 mm up . Remember though please be very safety concious if your having a look . I think for someone whose not sure its best to get someone in .Hope this helps , you will probably get a reply from my guru of electricity Mr Sparks as well , he is the man so listen good . Good luck Jeff
    Jeffmo
     
    Posts: 103
    Joined: Mon Apr 09, 2007 9:22 am
    Top

    Postby pdenni » Thu May 24, 2007 9:35 pm

    hi jeffmo

    dont mean to be picky but the calculation for 12kw without cable length or diversity is 52 amps.
    7.5kw is pretty much the most you could put on a 32amp breaker
    pdenni
     
    Posts: 15
    Joined: Thu May 24, 2007 6:43 pm
    Top

    Postby sparx » Fri May 25, 2007 3:44 pm

    For Jeffmo; thanx for compliment but won't get involved in this one, enough experts here already!
    BCNU SPARX
    sparx
     
    Posts: 2166
    Joined: Wed Mar 21, 2007 8:33 pm
    Location: The fifth continent.
    Top

    Postby Jeffmo » Fri May 25, 2007 6:14 pm

    Hi Sparks , ok obviously my estimate is without diversity or cable length , but as a rough estimate i think my calc are correct ,assuming a little diversity ,very little cos it should be on seperate circuit and assuming cable length . I'll leave the confussion for questioners to others from now on . was just tryin to keep it simple .Cheers Jeff
    Jeffmo
     
    Posts: 103
    Joined: Mon Apr 09, 2007 9:22 am
    Top

    Postby Jeffmo » Fri May 25, 2007 7:09 pm

    Basic calc as i know it : example =
    12.5 kw = Total current = P/U = 12500/240 = 52.08A
    The demand = the first 10A = 10+ 30% of remainder =
    30 x ( 52.08 - 10)/100 = 30 x 42.08 /100 = 12.624
    Plus allowance for socket outlet if fitted =5A hence answer of 10+ 12.264+5 = 27.264 therefore 30 amp protection will do , dependent on length of run ok ive said my peace thankyou .
    Jeffmo
     
    Posts: 103
    Joined: Mon Apr 09, 2007 9:22 am
    Top


    Post a reply

    11 posts • Page 1 of 1

    Return to Electrics





     


    • { RELATED_TOPICS }
      Replies
      Views
      Last post
    • Main switch tripping
      by russellfl » Tue Aug 28, 2012 10:08 am
      1 Replies
      155 Views
      Last post by ericmark View the latest post
      Tue Aug 28, 2012 9:43 pm
    • oil fired boiler tripping ring main
      by groobydoo » Sat Nov 24, 2007 1:47 pm
      4 Replies
      1247 Views
      Last post by TCSC View the latest post
      Sun Nov 25, 2007 5:06 pm
    • Ring main from 30A cooker feed!
      by rcxkid » Tue Apr 08, 2008 11:53 am
      1 Replies
      1079 Views
      Last post by sparx View the latest post
      Tue Apr 08, 2008 9:08 pm
    • Moving a cooker point 10" Right of old cooker point...
      by timeemit » Sat May 30, 2009 2:46 pm
      8 Replies
      1837 Views
      Last post by kbrownie View the latest post
      Sun Jun 07, 2009 11:18 pm
    • RCD tripping
      by Tim Louth » Mon Mar 24, 2008 5:54 pm
      1 Replies
      1020 Views
      Last post by ericmark View the latest post
      Mon Mar 24, 2008 10:14 pm

    • Board index
    • The team • Delete all board cookies • All times are UTC
    • SitemapIndex SitemapIndex
    • RSS Feed RSS Feed
    • Channel list Channel list
    Powered by phpBB ® Forum Software © phpBB Group





    Diy Doctor Ltd  (Company No. 5863375)

    DIY  |  DIY How To  |  DIY Forum  |  Terms & Conditions  |  Privacy Policy  |  Cookie Info  

    © Copyright DIY Doctor Ltd 2011  Developed by Boson Media  Hosted by Rackspace