Outside Socket


Postby Stillia » Mon Jul 13, 2009 6:08 pm

Hi there,

Fitted a double outside socket with integral RCD protection (spurred off ring main) & one of the sockets is not working, whilst other is fine. Checked with socket & see and indicates a neutral fault, so reterminated neutral & still showin same fault. Am I right in thinking that the unit is faulty??

Thanks, Andy.
Stillia
Rank: Apprentice
Progress to next rank:
47.4%
Posts: 14
Joined: Mon Dec 10, 2007 5:31 pm

Sponsor

Simply Build It

Postby kbrownie » Tue Jul 14, 2009 7:09 am

You can test the circuit is healthy by following test test procedures in guidance note 3 or the on-site guide.
Can't say for sure if you have a faulty accessory, circuit or test instrument.
but likely to be accessory by what you have stated.
Has this socket been installed be electrician or you, take a look on part p projects pages on this site.
I would have used an RCD protected spur at ring main as the additional cable that you have terminated is not RCD protected the way you have done it is likely not to comply to requirements.
KB
kbrownie
Rank: Project Manager
Posts: 1993
Joined: Mon Mar 05, 2007 9:36 pm

Postby sparx » Wed Jul 15, 2009 4:26 pm

only one set of terminals internally linked (or in this case , not) so unit must be faulty,
usual part P comments apply as any work outside house is notifiable as KB says,
sparx
Rank: Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 