Over pumping into header tank

Post by andrew fitzpatrick » Wed Jul 30, 2008 11:41 am

Can anyone help? Whenever my boiler is on I am getting hot water constantly running out of the vent pipe into the expansion tank for the central heating system.

Can I block the pipe without risk of blowing the system? If not can anyone suggest a method of stopping this happening?

The expansion tank is only mounted 1.5m above the pump nad motorized valves.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 5:22 pm

Post by htg engineer » Sun Aug 03, 2008 1:00 pm

DO NOT: blank or fit any valves to the vent pipe.