pressure loss


Postby gary10 » Mon Feb 25, 2008 3:59 pm

i have a halstead quattro combi boiler in the loft that keeps loosing pressure but every time i re pressurize the system water comes out of the overflow pipe outside can anyone advise please
gary10
Posts: 1
Joined: Mon Feb 25, 2008 3:45 pm

Sponsor

Simply Build It

Postby ALDA » Mon Feb 25, 2008 5:03 pm

FAULTY PRESSURE RELIEF VALVE
ALDA
Posts: 397
Joined: Mon Feb 04, 2008 8:15 pm


Postby htg engineer » Mon Feb 25, 2008 6:56 pm

It could be and sounds like a fault with the pressure relief valve,

What have you been taking the pressure to ?

the Presssure relief valve will normally open between 3.0 and 4.0 bar. If it's leaking outside - at 1.0 - 1.5 bar then replace the PRV and all should work fine.
htg engineer
Posts: 3193
Joined: Tue May 22, 2007 5:22 pm