protherm 80e no flame ie no flame.....
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

4 posts   •   Page 1 of 1
carl james
Labourer
Labourer
Posts: 3
Joined: Tue Oct 21, 2008 10:54 pm

protherm 80e no flame ie no flame.....

by carl james » Wed Oct 22, 2008 5:43 pm

I have a Protherm 80e combi, I have an F1 error code showing
(ie no flame) , i have checked the pump OK, cleaned out the water heat exchanger, replaced the 'bottle' air trap, checked the airflow sensor ok,
tested the micro switches ok, do you have any ideas ???? could it be
the gas valve control box??

ps..

when boiler is turned the pump starts, then after around 5 seconds the fan starts, this runs for approx 10-12 seconds then stops, the lcd shows
'F1' fault , after about 30 seconds the pump turns off ??????

thanks in anticipation

Carl...

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Thu Oct 23, 2008 12:53 pm

Check air pressure switch. Does the fan speed seem about right ?

If the connection in the air pressure switch is not made - the sequence cannot go any further - and the boiler will go to lockout.

htg

carl james
Labourer
Labourer
Posts: 3
Joined: Tue Oct 21, 2008 10:54 pm

by carl james » Thu Oct 23, 2008 9:29 pm

thanks for reply, read another post reply regarding the overheat trip
switch although all my litrature dosn't mention a trip I found one
and reset it , all working now chears.....

carl james
Labourer
Labourer
Posts: 3
Joined: Tue Oct 21, 2008 10:54 pm

by carl james » Mon Nov 03, 2008 6:10 am

Still getting an error, now I am getting an F0 fault (low flow).
I have replaced the pump and bled the system again. the pump
seems to be getting quite hot possibly overheating and cutting
out, if i remove the flow sensor and press the micro switch in the F0
warning goes out, after a while the pump re-starts ,could this be the diapragm faulty. any ideas????