radiator / boiler problem


Postby mrchristoph » Mon Mar 17, 2008 4:43 pm

I have changed a traditional radiator for a towel radiator in the bathroom. It is very hot at the bottom but not middle up, despite constant bleeding of valve. In fact, all upstairs radiators have been bled but water not coming out. NOW, boiler is making a windy noise as it is working which is very disturbing. The boiler is still working and all radiators/hot water ok. Any advice??
mrchristoph
Rank: Labourer
Progress to next rank:
75%
Posts: 4
Joined: Mon Mar 17, 2008 4:39 pm

Sponsor

Simply Build It

Postby Rico » Tue Mar 18, 2008 9:08 am

mrchristoph,

Can you tell us what heating system you have.

TYpe of boiler, do you have combi or cylinder.

Rico
Rico
Rank: Tradesman
Progress to next rank:
53.8%
Posts: 38
Joined: Wed Feb 27, 2008 11:55 am

Postby htg engineer » Tue Mar 18, 2008 6:03 pm

Type of boiler, you system is not full of water - when you open the bleed vent on the towel rail - water should be present.

Your system could need re-pressurising, or it could be airlocked or a blockage
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Postby mrchristoph » Wed Mar 19, 2008 5:26 pm

thanks, we have a combi boiler in a new house.
mrchristoph
Rank: Labourer
Progress to next rank:
75%
Posts: 4
Joined: Mon Mar 17, 2008 4:39 pm

Postby htg engineer » Thu Mar 20, 2008 9:27 pm

what's the pressure gauge reading ? (on the boiler) should be between 1.0 and 1.5 bar.

Read boiler manual - it should tell you how to re-pressurise system
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Postby mrchristoph » Fri Mar 21, 2008 4:49 pm

If only i could find the manual! will try to find on internet though
mrchristoph
Rank: Labourer
Progress to next rank:
75%
Posts: 4
Joined: Mon Mar 17, 2008 4:39 pm

Postby htg engineer » Fri Mar 21, 2008 9:11 pm

Boiler make and model ?

Is there 2 valves under the boiler capped or connected with a flexi hose ?
if there is - this is the filling loop,
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Postby mrchristoph » Sat Mar 22, 2008 1:29 pm

I am looking at the expansion vessel pressure valve which is at 0 whether heating is on or not. As per other topics have tried a bike pump but this is almost impossible to pump. in fact. when taking valve off more air seems to come out than i had got in.
mrchristoph
Rank: Labourer
Progress to next rank:
75%
Posts: 4
Joined: Mon Mar 17, 2008 4:39 pm

Postby htg engineer » Sat Mar 22, 2008 4:58 pm

Completely wrong - you're trying to re-pressurise with air - the system needs to be re-pressurised with water and not the expansion vessel (so don't try filling vessel with water).

Get a heating engineer out as you don't seem to have a clue how the system works - otherwise you're going to end up making a simple job into a bigger more expensive one.

You'll now also need to have expansion vessel pressure checked.
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 