radiators will not heat up


Postby freezingcoldjim » Tue Oct 28, 2008 8:29 pm

I have got a vented system. I have just drained, removed and flushed out my radiators. Now refitted and bled the system. I switched on I get hot water in the heating pipes as far as the radiators. Further bleeding lets hot water into the rads. but when left to their own devices the rads do not stay hot. Is there a possibility of an airlock on the return side, if so how do I shift it? To complicate matters further I live in a bungalow with 6 different central heating loops from the one pump.
freezingcoldjim
Posts: 1
Joined: Tue Oct 28, 2008 8:21 pm

Sponsor

Simply Build It

Postby htg engineer » Thu Oct 30, 2008 3:48 pm

Airlocked, try draining and refilling. Or try turning off all but one radiator and see if you get clear one at a time.

If no luck remove each radiator and open each valve to allow water to flow into a bucket, you will probably hear the air escape.


htg
htg engineer
Posts: 3193
Joined: Tue May 22, 2007 5:22 pm