ring mane trips


Postby jamespond1 » Fri Jul 31, 2009 6:28 pm

hi, i have installed a ring main upstairs and one downstairs. the problem is my downstairs ring is tripping the rcd, i have checked all 9 sockets all cables are correct and earths insulated i have used a fluke to check the ring is correct and i do get continuity. can some body give me any advice.
many thanks james.
jamespond1
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Fri Jul 31, 2009 6:03 pm

Sponsor

Simply Build It

Postby kbrownie » Sat Aug 01, 2009 2:40 pm

Have you notified building controls under part p installing a new circuit
kbrownie
Rank: Project Manager
Posts: 1993
Joined: Mon Mar 05, 2007 9:36 pm

Postby sparx » Sat Aug 01, 2009 4:41 pm

Have you checked Neutrals on same RCD supply as lives for ring? presume you have split load board with 2 rcd's
If not that then check for N-E fault, often front plate screw of socket pressing on N in back box,
regards Sparx
sparx
Rank: Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 