ring mane trips

by jamespond1 » Fri Jul 31, 2009 7:28 pm

hi, i have installed a ring main upstairs and one downstairs. the problem is my downstairs ring is tripping the rcd, i have checked all 9 sockets all cables are correct and earths insulated i have used a fluke to check the ring is correct and i do get continuity. can some body give me any advice.
many thanks james.

kbrownie
Project Manager
Project Manager
Posts: 1995
Joined: Mon Mar 05, 2007 9:36 pm

by kbrownie » Sat Aug 01, 2009 3:40 pm

Have you notified building controls under part p installing a new circuit

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sat Aug 01, 2009 5:41 pm

Have you checked Neutrals on same RCD supply as lives for ring? presume you have split load board with 2 rcd's
If not that then check for N-E fault, often front plate screw of socket pressing on N in back box,
regards Sparx