Shower Blowing a fuse


Postby Kate » Fri Mar 23, 2007 8:48 pm

Hi guys, the site was recommended to me but you will have to excuse my ignorance - I am female after all - have just fitted a new shower 10.5kw? and a straight swap for my old one an 8.0 kw? only problem is every time you turn it on to hot water it blows a fuse - kinda need some help and advice - thanx :cry:
Kate
Posts: 1
Joined: Fri Mar 23, 2007 8:41 pm

Sponsor

Simply Build It

Postby sparx » Sun Mar 25, 2007 9:17 pm

Without getting all mathsy.....
each kWatt draws around 4.2 Amps from supply,
SO.......8 x 4.2A =33.6A.
and......10.5 x 4.2A=44.1A
i,m guessing you have a 40 A. fuse fitted?, will your circuit cable take a larger fuse rating, how large is the cable?, how far from fuse board to shower in meters ? you need a friend in the trade,
(qualified Electrician, not the bloke down the pub)hi,
as temp measure if shower has 2 settings try lower one to see if fuse blows, it should not,
Sparx
sparx
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.


Display posts from previous
Sort by
Order by


 


  • Related Topics