Paul Baker
Labourer
Labourer
Posts: 1
Joined: Tue Aug 28, 2007 5:55 pm

Spur off Smoke Alarm

Post by Paul Baker » Tue Aug 28, 2007 6:10 pm

Hi
Can you take an electrical spur off a smoke alarm circuit, the spur would be used to power an TV signal booster input =230v - 50Hz 0.06A? Also what is the wiring colour code: brown = live, grey = ?, black = ?, copper = earth

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

Post by sparx » Wed Aug 29, 2007 7:59 pm

Hi, No you can't spur off smoke alarms, the wiring you have seen there is Live, Neutral, common alarm signal to link all together & earth which should have green/yellow sleeving on the bare copper.
Not everyone using same colours either! Live Brown is standard but regs recommend Grey be sleeved Blue as Neutral, & Black is sleeved brown as interconnecting core but as I say no standard.
regards Sparx