testing radial circuits


Postby blue fish » Wed Aug 29, 2007 9:42 pm

how do i test a radail circuit ie a ring is circuit R1+R2

kind regards blue fish
blue fish
Posts: 1
Joined: Wed Aug 29, 2007 9:36 pm

Sponsor

Simply Build It

Postby sparx » Thu Aug 30, 2007 8:12 pm

Hi, radial easier to test as no L-L, N-N, E-E tests just test L-E with furthest socket L-E connected together which is r1+r2. Exactly the same as testing a lighting circuit. Also with a radial r1+r2 added to Ze at consumer unit should approx. = Zs earth loop impedance reading taken at same socket when connected up properly and livened up.regards