Triple 2-way light switch
Ask questions and find answers to many subjects relating to electrics and electrical work

2 posts   •   Page 1 of 1
forumsetc
Labourer
Labourer
Posts: 2
Joined: Wed Jul 21, 2010 4:36 pm

Triple 2-way light switch

by forumsetc » Wed Jul 21, 2010 5:04 pm

As the old triple 2-way switch in the hall was cracked I have had to replace it. The 3 switches on the light switch served the outside security light, the hall and a 2-way switch for the upstairs hall. The switch was around 30 years old and looking at it from the back left to right at the top had L1 (yellow with red sleeve) L2 (blank), COM (blue with red sleeve), L1 (red) and L2 (blue with red sleeve). At the bottom it had COM (red), L1 (connected to the same red from the COM), L2 (blank) and COM (yellow with red sleeve).
The replacement 10 amp triple 2 way light switch has a different layout, having at the top (with my connections which I tried to copy across from the old switch), again looking at the back left to right, L2 (blank), L1 (yellow with red sleeve), L2 (blank), L1 (red), L2 (blue with red sleeve) and L1 (red). At the bottom COM (blue with red sleeve), COM (yellow with red sleeve) and COM (red going to the final L1 on the right, again looking at the switch from the back).
Everything works to an extent. Looking at the switch from the front (left to right) the left switch switches on/off the upstairs hall, but only if the upstairs switch is set to ON. The middle switch works as expected for the downstairs hall. The right switch for the outside security lightworks the wrong way round, i.e. it is ON if in the switch is in the OFF position and OFF if it is in the ON position.
I would appreciate help in getting the 2-way to the upstairs hall to work properly irrespective of the upstairs switch being in the ON or OFF position and to get the security light switch to be ON when switched ON and OFF when switched OFF.
Thanks to anyone who can help.

forumsetc
Labourer
Labourer
Posts: 2
Joined: Wed Jul 21, 2010 4:36 pm

by forumsetc » Thu Jul 22, 2010 4:05 pm

Problem solved once I discovered that both old and new switches are essentially the same in having a triangular COM, L1, L2 structure albeit with a different layout. Once I replicated the triangular cabling from the old switch everything worked exactly as expected although I had to experiment a little in switching the terminals for the 2 yellow with red sleeves cables and then doing the same for the 2 blue with red sleeve cables.