Under Tub - outside all zones


Postby misterg » Mon Jul 23, 2007 8:23 pm

Hi

I've had conflicting advice on what can be put in under the bathtube. The sides cannot be removed without using a tool, so my understanding is this is outside all zones.

i'm lookin to get a shower pump fitted.

Can a socket be put under a bath for the pump, or should it be connected to an FCU outside the bathroom.

Also been told it can only be a low voltage pump - is this correct?

Cheers

Mister G
misterg
Posts: 49
Joined: Sat Jun 23, 2007 8:58 pm

Sponsor

Simply Build It

Postby BLAKEY1963 » Mon Jul 23, 2007 10:53 pm

[quote="misterg"]Hi

I've had conflicting advice on what can be put in under the bathtube. The sides cannot be removed without using a tool, so my understanding is this is outside all zones.

i'm lookin to get a shower pump fitted.

Can a socket be put under a bath for the pump, or should it be connected to an FCU outside the bathroom.

Also been told it can only be a low voltage pump - is this correct?

Cheers

MISTERG
IDEALLY ( OF COURSE YOUR PART P SPARK WILLADVISE )
I WOULD PUT THE PUMP UNDER THE BATH AND PUT THE
SUPPLY TO IT UNDER FLOOR BOARDSTO RCD SPUR OUTSIDE
BATHROOM. MOST OF THE THESE PUMPS ARE STEP DOWN VOLTAGES ANYWAY.
BLAKEY1963

Mister G[/quote]
BLAKEY1963
Posts: 654
Joined: Wed Jun 13, 2007 10:57 pm


Postby misterg » Mon Jul 23, 2007 11:50 pm

Thanks Blakey.

If the ring main will be on the CU RCD, do I need another one, or will an FCU be sufficient?

Cheers

Mister G
misterg
Posts: 49
Joined: Sat Jun 23, 2007 8:58 pm


Postby sparx » Tue Jul 24, 2007 11:21 am

Hi, guess BLAKEYS working !! HI, Hi,
yup if ring on rcd then just FCU suffices, but under current regs [this year anyway] must take 4mm earth from FCU to local pipes, & as most pumps are placky link across incoming to outgoing pipes, regards SPARX
sparx
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.


Postby Stephen the sparks » Tue Jul 24, 2007 8:20 pm

Under the tub is actually zone 0. Must be IPX7 protection, only 12v SELV equipment is allowed that cannot be reasonably located elsewhere.

No switchgear allowed in zone 0 I am afraid.

Regs 601-08-01 and 601-09-01 apply
Stephen the sparks
Posts: 9
Joined: Tue Jul 24, 2007 7:20 pm


Postby misterg » Tue Jul 24, 2007 11:33 pm

[quote="Stephen the sparks"]Under the tub is actually zone 0. Must be IPX7 protection, only 12v SELV equipment is allowed that cannot be reasonably located elsewhere.

No switchgear allowed in zone 0 I am afraid.

Regs 601-08-01 and 601-09-01 apply[/quote]

Hi

I thought Zone 0 was in the tub and if you need a tool to remove side of tub then it is outside all zones.

Is this not correct?

Also what is IPX7?

Cheers

G
misterg
Posts: 49
Joined: Sat Jun 23, 2007 8:58 pm


Postby misterg » Tue Jul 24, 2007 11:39 pm

[quote="sparx"]Hi, guess BLAKEYS working !! HI, Hi,
yup if ring on rcd then just FCU suffices, but under current regs [this year anyway] must take 4mm earth from FCU to local pipes, & as most pumps are placky link across incoming to outgoing pipes, regards SPARX[/quote]

Cheers Sparx

Great that was what I was hoping for.

I'll make sure the electrician fits the 4mm earth too.


Regards

G
misterg
Posts: 49
Joined: Sat Jun 23, 2007 8:58 pm