Victoria Plumb - Sale now onThe UK's leading online supplier of bathrooms and bathroom accessories are committed to the supply of luxury and top quality products at unbeatable prices. Victoria Plumb also pride themselves on their customer service and ensure that visitors receive all the advice, help and support they will need in order to create the bathroom of their dreams.

Victoria PlumbClick through to the Victoria Plumb website and take advantage of their fantastic sale, with savings of up to 60%. There has never been a better time to replace your bathroom!




Are you a tradesman ? Get your very own webpage with ProblemSolved all for FREE - Click here

Check the DIY Projects pages for your answers before posting your questions..They come with pictures !!




Share and bookmark DIY Doctor

Link to DIY Doctor - Click Here RSS news feed DIY Doctor RSS Feed  Email Bookmark and Share
 

Pressure Loss On Combi Bolier

 
Post new topic   Reply to topic    Diy Doctor Forum Index -> Plumbing
View previous topic :: View next topic  
Author Message
Bimboveloce



Joined: 27 Oct 2009
Posts: 8

PostPosted: Fri Nov 06, 2009 11:49 am    Post subject: Pressure Loss On Combi Bolier Reply with quote

Hi I have a Potterton Performa Combi boiler approx 6 years old, regulalry serviced. Probem is I keep losing pressure when the central heating is run, no issues on hot water only.

The wife had the central heating on for a couple of hours yesterday and the bolier lost nearly half a bar. Normaly have it set at 1.5 when cold

I have checked all my bleed valves, connections, drain taps etc for leaks and cant see any problems.

Where can the problem be, is is the boiler, the pipework? please help got 2 young kids and i need the heating on.

Mnay thanks
Tony
Back to top
View user's profile Send private message
htg engineer



Joined: 22 May 2007
Posts: 2628

PostPosted: Fri Nov 06, 2009 8:51 pm    Post subject: Reply with quote

With the heating on, does the pressure rise to above 3 bar?

Check PRV discharge, any leaks ?


htg
Back to top
View user's profile Send private message
rosebery



Joined: 26 Sep 2007
Posts: 1819

PostPosted: Fri Nov 06, 2009 11:48 pm    Post subject: Reply with quote

Pressure/expansion vessel may need pumping up or the diaphram may be split.

Cheers
Back to top
View user's profile Send private message
Bimboveloce



Joined: 27 Oct 2009
Posts: 8

PostPosted: Mon Nov 09, 2009 9:53 am    Post subject: Reply with quote

I can say i have checked what the pressure is when the boiler is producing hot water and central heating, i will have a look. As for the PRV seems to have collected some water from it, about 1inch in the bottom of a coke can.
How can i check the pressure/expansion vessel or if the diaphragm is split?
Regards
Tony
Back to top
View user's profile Send private message
Bimboveloce



Joined: 27 Oct 2009
Posts: 8

PostPosted: Mon Nov 09, 2009 10:53 am    Post subject: Reply with quote

FURTHER UPDATE
Wife says heating has been on for 1hr, pressure is just over 2bar. When the bolier fires up the pressure goes up until is turns off and the reading is now 2.6, (in to the red zone) maybe why i am getting water from the PRV, but why is the pressure rising so much and into the red. Normal cold pressure is 1.5bar

Thanks
Tony
Back to top
View user's profile Send private message
htg engineer



Joined: 22 May 2007
Posts: 2628

PostPosted: Mon Nov 09, 2009 7:21 pm    Post subject: Reply with quote

Try re-pressuring the expansion vessel. Release pressure from system, using a foot pump, pressurise to 1 bar.


htg
Back to top
View user's profile Send private message
Bimboveloce



Joined: 27 Oct 2009
Posts: 8

PostPosted: Tue Nov 10, 2009 11:36 am    Post subject: Reply with quote

Thanks HTG for your reply.
Maybe silly question to ask but how do i re-pressurize the expansion vessel, where do i connect the foot pump and do i use the pressure gauge on the pump for reference?
Back to top
View user's profile Send private message
htg engineer



Joined: 22 May 2007
Posts: 2628

PostPosted: Wed Nov 11, 2009 8:30 pm    Post subject: Reply with quote

There'll be a schraeder valve on the expansion vessl (like a car tyre) connect foot pump, and pump to 1 bar (on the foot pump gauge) then refill system.

If there's any water when the schraeder valve is pressed, the expansion vessel needs replacing.


htg
Back to top
View user's profile Send private message
Bimboveloce



Joined: 27 Oct 2009
Posts: 8

PostPosted: Mon Nov 16, 2009 1:21 pm    Post subject: Reply with quote

Guy's I will try and pressure the expansion vessel and see if there is any water in it. I will let you know.

Whats the average cost to replace the expansion vessel if needed?

Regards

Tony
Back to top
View user's profile Send private message
Bimboveloce



Joined: 27 Oct 2009
Posts: 8

PostPosted: Tue Nov 24, 2009 10:05 am    Post subject: Reply with quote

Hi HTG,
I released the pressure from the boiler by twisiting the PRV until the gauge said zero, i then repressurised the expansion chamber with a foot pump as your suggested to 1bar and repressuresed the system. Boiler is working fine, pressure seems constant and with no loss. I will continue to monitor and hope the issue is resolved, if not I will be back on.

HTG engineer many thanks for your help, it has been invaluable.

Regards

Tony
Back to top
View user's profile Send private message
Display posts from previous:   





Post new topic   Reply to topic    Diy Doctor Forum Index -> Plumbing All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum



Powered by phpBB © 2001, 2005 phpBB Group