when hot water on heating is too although not selected 2b

by wired1 » Thu Jun 26, 2008 8:50 pm

:( Either by using the timer or manual selection, when the hot water is on the heating now comes on even though it hasn't been selected. The timer/control unit only shows the hot water as being on. Is this a faulty timer/control unit :?:

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Fri Jun 27, 2008 9:11 am

Possibly - but more likely to be a faulty motorised valve.

The motorised valve sits on top of a three port valve. You have flow from boiler AB, Central Heating port A, Hot Water port B.

When CH only is selected the motor turns to open one port A, HW only selected it will turn to open the other port B. HW and CH it will open ports A and B.

Also check 3 port valve spindle turns freely.

htg

wired1
Labourer
Labourer
Posts: 2
Joined: Thu Jun 26, 2008 8:44 pm

actuator problems?

by wired1 » Sat Jun 28, 2008 4:00 pm

Thanks for that. I have located the actuator - cleverly placed so that it is tightly fitted onto the 3 pins of the pipework and between a joist. I can't see the make, begins with Lys...... I think - unit about 16 years old!. At the side a black lever 'was' almost hanging out of the case but as I got hold of it, it pushed into the case and I can't get it free now. The radiators are very hot but I'm assuming that this is becaue there is no thermostatic control over them due to the heating not actually being selected via the timer unit. Would this be correct? If I remove the actuator - white box - do I have to close off the water supply via the various pipes to the unit or is it just a case of taking it off? I understand how the motorised bit works the valves but I'm not sure what is actually faulty and how the components of the actuator physically work the pipework connection.